Thanks guys.. ok a "little" more here then...
Firstly, when I say it falls between domestic and commercial... I only meant in terms of the kind of electrician who would deal with it. Too complicated for a lot of domestic only electricians (including me probably) and not big enough for most commercial oriented companies.
It is currently economy 10, 3 phase with one 3phase meter in the DNO cut-out - 3x 80A fuses (I believe although I can't check). 5 Tails go through the wall to an internal "cutout" (it isn't really, but I will call it that for ease) There are the three lines and neutral which go to henley blocks, then from there two outs;
1 -> 30mA RCD switch ->contactor (which I have replaced when it shorted & fried) which has the off peak switched line from the meter -> off peak 3phase board (DB-A) around 8m away (one of 5 DBs in understairs cupboard) via two T&E cables 16mm2 I think although I need to check. This feeds the main heating demand for 7 night storage heaters + the aga.
2 -> seperate 30mA 3ph RCD -> DB-E via 16mm SWA .
This currently feeds permanent live feed to the 7 storage heaters + the aga... As well as (I suspect**) the other 3 single phase boards
Understairs electrical cupboard we have 3 more single phase boards with various sockets & lighting. These 5 boards are mounted on a large piece of ply with cabling behind so not easy to see without dismantling.
** So far I have not assessed the details of the current wiring as that will be a fair chunk of time to strip down and figure out exactly what goes where.
This all started when the contactor controlling the heating shorted out and went crispy blowing the main fuse twice. They then called me and after I identified the smoking switchgear was told "Ah yes, I did smell burning but my husband said it was nothing". Anyway. this was in the winter so I sourced and replaced the 90A contactor and it all seems to be fine again.
This incident (and their £1200 electricity bill) caused them to rethink everything and the plan now (after a little encouragement) is to come off economy 10, replace 7 old inefficient night storage heaters with new electric rads, replace old aga with newer more efficient one. Replace water heater with two new immersion tanks (2x6kw) which will actually be more but they want the extra capacity. They also want a new 32A induction hob fitted. They also want to lay in provision for a sizable 'garage conversion' which hasn't got to the planning stage yet.
I will replace all the 5 consumer units with one (or maybe 2 if required) - these will run all lighting & sockets as well as the storage heaters and aga, as well as a new c/u in the garage.
I need to do a full assessment of the current C/Us sockets & lights but also trying to start a rough plan of how to distribute things.
Not having had a whole lot of experience designing 3-phase installations like this I am keen to get input.
I am thinking use 16mm 3-phase XLPE SWA from 30mA RCD straight to new boards in understairs cupboard. Take one phase from understairs cupboard to new garage consumer unit using SWA which will run outside. This will power the 2x6kw immersions plus extension sockets & lights. It would be physically easier to power the new induction hob from here too, but worried about load. They haven't as yet confirmed requirements for extension but I'm assuming at least 1 final ring circuit and 2 lighting.
The new radiators total actual potential draw is about 85A, but having each rad on a breaker will mean a nominal breaker total of 110A - it seems to depend on who you ask as to how to come up with max load / diversity, however you look at it, that is the best part of a whole phase, leaving around 80A for the sockets, lights & aga
I would like opinion on any of this, but specifically how to distribute the load - I don't really want to buy new 3phase boards - the two that are already there seem fairly new and adequate. I would like to run single phase to the garage to save putting a 3-phase board there and to save running 5-core out there, but my gut says easier to balance the phases if there is a 3-ph board in the garage too.
OK - this post is clearly long enough. I'm sure there will be questions which I will do my best to answer.
Thanks for making it to the end!
I think I am prepared for the torrent of question, humour and hopefully useful suggestions to come!...