it's not 30kw at all- 5*4 wouldv'e done
anyhow you could fit a sub-board with your 16s
anyhow you could fit a sub-board with your 16s
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 3 phase help. in the Electrician Talk | All Countries area at ElectriciansForums.net
it's not 30kw at all- 5*4 wouldv'e done
anyhow you could fit a sub-board with your 16s
google electrolux air o steam level b combi lw 6 gn 1/1 electric and see tech details
ya 5 by 4
just make sure you connect the right end to the cooker-otherwise it'll cool instead of heating
ask the wholesalers to mark the start and finish on the cable
Just looked at link...... If it's a 6 grid 1/1 it's a baby and they only pull about 10 amps mate
i calculate nearer 15amp for 10.1 kw-but still
i'd run 4 myself but 2.5 would prob do
im confused.com now. im not sure what u mean by start and end of cable. also every spark ngives a different answer to the cable size and how many amps the cooker will pull. bloddy hell
lol
He was taking the pish mate !!
Ok, here is how it goes
20a Type c 3ph breaker, 6mm 4 or 5 core (+/-cpc), 45a rotary isolator, 6mm to oven use all SWA and use CW glands(ip rated)
Ill ask again, will there be a catering engineer there to commision as they are a sod !
thanks mate. i only av to supply up to the rotary switch.iv got 16mm cable 4 core ans seperate 16mm earth wire. we bought 16mm as we were gona put a 3 phase board as the owner also wanted a 3 phase chiller. so my cable is too big but who cares, im not paying 4 it. tanx. wat tests will i need to do on that install