im confused.com now. im not sure what u mean by start and end of cable. also every spark ngives a different answer to the cable size and how many amps the cooker will pull. bloddy hell
 
im confused.com now. im not sure what u mean by start and end of cable. also every spark ngives a different answer to the cable size and how many amps the cooker will pull. bloddy hell


lol

He was taking the pish mate !!

Ok, here is how it goes

20a Type c 3ph breaker, 6mm 4 or 5 core (+/-cpc), 45a rotary isolator, 6mm to oven use all SWA and use CW glands(ip rated)

Ill ask again, will there be a catering engineer there to commision as they are a sod !
 
thanks mate. i only av to supply up to the rotary switch.iv got 16mm cable 4 core ans seperate 16mm earth wire. we bought 16mm as we were gona put a 3 phase board as the owner also wanted a 3 phase chiller. so my cable is too big but who cares, im not paying 4 it. tanx. wat tests will i need to do on that install


lol

He was taking the pish mate !!

Ok, here is how it goes

20a Type c 3ph breaker, 6mm 4 or 5 core (+/-cpc), 45a rotary isolator, 6mm to oven use all SWA and use CW glands(ip rated)

Ill ask again, will there be a catering engineer there to commision as they are a sod !
 
thanks mate. i only av to supply up to the rotary switch.iv got 16mm cable 4 core ans seperate 16mm earth wire. we bought 16mm as we were gona put a 3 phase board as the owner also wanted a 3 phase chiller. so my cable is too big but who cares, im not paying 4 it. tanx. wat tests will i need to do on that install

R1+R2 and Ir mate, only IR to the rotary switch and im afraid you have absolutely no chance of getting 16mm 4 core terminated in the oven, i would buy a 3mtr length of 6mm for that!

I hate to keep asking but who is commisioning the oven ?? because these things need setting up by the installer on first power up, and involve all sorts of set up and calibration, i know on the far superior Rationals it takes about a hour and thats if you know what you are doing!

What size breaker do you have for this and what type is it??

Also the cable from rotary to oven will need to be 5 core as there is absolutely no way of terminateing a seperate earth to these ovens! having said that most ove these ovens are 3ph only and do not require Neuteral, if this is the case do away with the 16mm supp earth, and use the 4th core as cpc, again all of this needs confirming before arrival on site
 
Last edited:
thanks mate. i only av to supply up to the rotary switch.iv got 16mm cable 4 core ans seperate 16mm earth wire. we bought 16mm as we were gona put a 3 phase board as the owner also wanted a 3 phase chiller. so my cable is too big but who cares, im not paying 4 it. tanx. wat tests will i need to do on that install

Check rating and condition of existing equipment including that of the distributor to confirm it is suitable for the additional load. Check adequacy of existing earthing and bonding arrangements, upgrade if not adequate.

Test R1+R2 of the new circuit, insulation resistance between all conductors, and confirm polarity.
Energise circuit, and immediately confirm polarity and verify phase sequence.
Measure Zdb at the distribution board for your circuit, add this to the R1R2 to calculate Zs.
At DB, measure PEFC. Measure PSSC and multiply this by square root of 3 to calculate prospective three phase fault current. Verify your breaker is adequately rated for this.
Verify voltage drop between origin of installation and the isolator you have installed with the load connected.
Complete and sign the Electrical Installation Certificate.
 
seems ur all enjoying the funny answers but hey i dont care. we had to start at the begining. mate the company supplying the oven will do all work after the rotary switch. the company asked for a 3p and n supply.


R1+R2 and Ir mate, only IR to the rotary switch and im afraid you have absolutely no chance of getting 16mm 4 core terminated in the oven, i would buy a 3mtr length of 6mm for that!

I hate to keep asking but who is commisioning the oven ?? because these things need setting up by the installer on first power up, and involve all sorts of set up and calibration, i know on the far superior Rationals it takes about a hour and thats if you know what you are doing!

What size breaker do you have for this and what type is it??

Also the cable from rotary to oven will need to be 5 core as there is absolutely no way of terminateing a seperate earth to these ovens! having said that most ove these ovens are 3ph only and do not require Neuteral, if this is the case do away with the 16mm supp earth, and use the 4th core as cpc, again all of this needs confirming before arrival on site
 
seems ur all enjoying the funny answers but hey i dont care. we had to start at the begining. mate the company supplying the oven will do all work after the rotary switch. the company asked for a 3p and n supply.

U aint got a problem if u aint gotta connect the unit up!

Its a simple circuit then, and good news about the commisioning as its a nightmare!!

Make sure that you use a type c breaker as these things dont half pull on start up and as you are using massively oversized cable then make sure the breaker is the right size(20a) so you are de-rating the circuit
 
tanx mate.happy monday comming i hope.

U aint got a problem if u aint gotta connect the unit up!

Its a simple circuit then, and good news about the commisioning as its a nightmare!!

Make sure that you use a type c breaker as these things dont half pull on start up and as you are using massively oversized cable then make sure the breaker is the right size(20a) so you are de-rating the circuit
 
Check rating and condition of existing equipment including that of the distributor to confirm it is suitable for the additional load. Check adequacy of existing earthing and bonding arrangements, upgrade if not adequate.

Test R1+R2 of the new circuit, insulation resistance between all conductors, and confirm polarity.
Energise circuit, and immediately confirm polarity and verify phase sequence.
Measure Zdb at the distribution board for your circuit, add this to the R1R2 to calculate Zs.
At DB, measure PEFC. Measure PSSC and multiply this by square root of 3 to calculate prospective three phase fault current. Verify your breaker is adequately rated for this.
Verify voltage drop between origin of installation and the isolator you have installed with the load connected.
Complete and sign the Electrical Installation Certificate.

Don't understand the references to checking polarity, unless you mean ensure the neutral supply wire and not a live wire is put into the neutral terminal in the rotary switch, but then I know practically nothing about three-phase. And I can understand the test for correct phase sequencing in a 3ph motor - but will the three phases be split inside the oven, one for each module (boiler, oven 1, oven2), or do 3ph ovens work differently to that?
 
don't know much but the majority of the load is a 9kw boiler-that may well be a 3*3KW star -connected load


any fans may be single phase so rotation is prob not an issue here

neutral is a 'live' wire btw
 
Last edited by a moderator:

Reply to 3 phase help. in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
667
Thanks :) Yes, of course, a 3P MCB... just didn't get the terminology correct. Many thanks for the reply
Replies
2
Views
1K
  • Question
Ok Dave thanks, no more accidents yet 🙏😂….
    • Like
    • Informative
    • Winner
Replies
6
Views
2K
  • Question
Thanks very much for that reassurance. Yes, this thread has got out of hand! Verb sap!
2 3
Replies
54
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks