L
lamb
thanks mate. i only av to supply up to the rotary switch.iv got 16mm cable 4 core ans seperate 16mm earth wire. we bought 16mm as we were gona put a 3 phase board as the owner also wanted a 3 phase chiller. so my cable is too big but who cares, im not paying 4 it. tanx. wat tests will i need to do on that install
Check rating and condition of existing equipment including that of the distributor to confirm it is suitable for the additional load. Check adequacy of existing earthing and bonding arrangements, upgrade if not adequate.
Test R1+R2 of the new circuit, insulation resistance between all conductors, and confirm polarity.
Energise circuit, and immediately confirm polarity and verify phase sequence.
Measure Zdb at the distribution board for your circuit, add this to the R1R2 to calculate Zs.
At DB, measure PEFC. Measure PSSC and multiply this by square root of 3 to calculate prospective three phase fault current. Verify your breaker is adequately rated for this.
Verify voltage drop between origin of installation and the isolator you have installed with the load connected.
Complete and sign the Electrical Installation Certificate.