Hello all
I am working for a company and we are installing supplies to some industrial 3 phase heaters in a factory in Devon.
I am questioning the maths used by my boss to arrive at the SWA size to supply these heaters.

Seeing as I am not a wiz with 3 phase stuff (only just started working for this firm), can someone give me some pointers on calculating the load?
I know the basics, but would like to make sure I am right before rocking the boat!

We are supplying 4x 15000kw heaters - 3 phase.
What load is that going to be per phase, per heater? He has basically divided the 15000kw into 3 - therefore 5kw per phase, then divided it by 230v.
Arriving at 21.7A per phase.

That means with 4x 3 phase heaters on the distribution board, we are looking at around 88A per phase load.
That's a huge 348A load.

He has 'guessed' at a 35mm 4 core SWA for the 50M run. Not convinced any calcs have gone into that decision.

Thanks!
 
Cock ups... wow, where to begin....

Installing a single phase board in a factory where most of the machines were 3 phase.
Running a huge bundle of cat5e cables in the same trunking as the supplies to the office ring circuits (for about 25M)
Installing a 3 phase SWA and isolator in a garage, and telling the customer to order a 3 phase oven... then I turn up to connect the oven and its only single phase at the incoming.
Frying the entire AV system in a house by fiddling around with things he doesn't understand behind a AV distribution system... and accidentally switching the voltage to 110v (how the hell he did that I don't know).

... just a few things make me worry

[ElectriciansForums.net] 3 phase loading question....
 
If your been payed your wage then ok as non of this is on your shoulders but as others have said look for another job... you seem the brightest in the whole company yet your only have a few yrs experience which worries me to the competence of your work colleagues.
 
I am putting way more hours than I am paid to sort out all sorts of messes they leave.
I just can't do work to their shoddy quality.
No - its not really my problem, its theirs.... but if I am installing it... I want it right.
I have NO IDEA how they ever pass their Niceic inspections.
Only been with them for 4 months... and not many more hopefully
 
I am putting way more hours than I am paid to sort out all sorts of messes they leave.
I just can't do work to their shoddy quality.
No - its not really my problem, its theirs.... but if I am installing it... I want it right.
I have NO IDEA how they ever pass their Niceic inspections.
Only been with them for 4 months... and not many more hopefully
listen...
i used to work for this fella and he was one of the biggest emptyheads goin...

no i mean it...this guy thought RCDs detected overcurrent
total spacker...the things he did & came out with...i used to despair of it..i really did...
 
I am putting way more hours than I am paid to sort out all sorts of messes they leave.
I just can't do work to their shoddy quality.
No - its not really my problem, its theirs.... but if I am installing it... I want it right.
I have NO IDEA how they ever pass their Niceic inspections.
Only been with them for 4 months... and not many more hopefully

These are one of things that you will eventually learn grasshopper
Its the individual that matters,its not the parasite that preys on him
 
Tony , what a top site . That one has gone straight on my favorites bar ! :punk:

At least one person appreciated it. That’s OK by me.

In the future that needle is going to swing further to the left. It may go below legal limits but it will never get to “total shutdown”.

Selective load shedding is in place and has been for several years. A plant I worked on could at a signal from UKPN shed 16MW of load within 20 minutes. More with advance notice.
 
I think our OP switch the heaters on this morning at 07:30 never seen Dynamic Demand so low before. 49.85 Hz.

As an idea, when you’re late for work “the alarm clock was late going off”, blame it on the grid frequency slowing down!
Somehow I don’t think it will wash as an excuse.
 
tony introduced me to this dynamic loading website a few weeks back when him and I were on the phone...
so it was a good little experiment when phil davies came round last weekend for me to get my power quality analyzer out stick it on frequency and check it up against the website...
on the nail...
 

Reply to 3 phase loading question in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Hello All, This is Vaithees from India. We are using an IR heater for a vacuum & non-vacuum chamber and got a heater from Chinese company and its...
Replies
0
Views
257
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
857

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top