Hello all
I am working for a company and we are installing supplies to some industrial 3 phase heaters in a factory in Devon.
I am questioning the maths used by my boss to arrive at the SWA size to supply these heaters.
Seeing as I am not a wiz with 3 phase stuff (only just started working for this firm), can someone give me some pointers on calculating the load?
I know the basics, but would like to make sure I am right before rocking the boat!
We are supplying 4x 15000kw heaters - 3 phase.
What load is that going to be per phase, per heater? He has basically divided the 15000kw into 3 - therefore 5kw per phase, then divided it by 230v.
Arriving at 21.7A per phase.
That means with 4x 3 phase heaters on the distribution board, we are looking at around 88A per phase load.
That's a huge 348A load.
He has 'guessed' at a 35mm 4 core SWA for the 50M run. Not convinced any calcs have gone into that decision.
Thanks!
I am working for a company and we are installing supplies to some industrial 3 phase heaters in a factory in Devon.
I am questioning the maths used by my boss to arrive at the SWA size to supply these heaters.
Seeing as I am not a wiz with 3 phase stuff (only just started working for this firm), can someone give me some pointers on calculating the load?
I know the basics, but would like to make sure I am right before rocking the boat!
We are supplying 4x 15000kw heaters - 3 phase.
What load is that going to be per phase, per heater? He has basically divided the 15000kw into 3 - therefore 5kw per phase, then divided it by 230v.
Arriving at 21.7A per phase.
That means with 4x 3 phase heaters on the distribution board, we are looking at around 88A per phase load.
That's a huge 348A load.
He has 'guessed' at a 35mm 4 core SWA for the 50M run. Not convinced any calcs have gone into that decision.
Thanks!