Hi I'm after some advice, ive been asked to connect up a new outbulding at a school, there was a building there before and the 4 core 16mm SWA was already in place. It will be a kind of extra classroom/club room and will have several sockets, lights and a small water heater in the toilet. Heating for the rest of the building isnt decided yet. I plan on fitting a 4 way 3 phase board and running everthing on seperate RCBOs. Probably 2 for lights, 2 for sockets, 1 for water heater and 1 for a fire alarm system. All circuits will obviously be 230v
My question is about the earthing. I thought about exporting the earth (main building TNCS) but im not sure the armour of the cable will be sufficiant. The main cable has also been joined including the armour. There are some main utilitys running under the building so if i TT it i know im going to drive the earth rod in to something! It also means putting a main RCD switch in and this will also mean ill have to try and find a double insulated gland to run the SWA into the board.
Any advice on this would be greatly appreciated.
 
Hi - with 16mm 4 core swa it's likely the armour will be sufficient for the CPC of the distribution circuit. But if there are any extraneous conductive parts in the 2nd building then it won't be big enough for protective bonding back to the installation MET in TNCS.
 
Maybe a silly question but why 3 phase?
Would single phase not do for what you are intending to install?
This is a good option depending on the phase balancing of the installation. Then if required you could use the spare conductors for bonding etc.
 
Tt is gland swa onto paxolin plate then bolt to base of dB and run earth straight from dB usaly 1 rod will get you around 30-40 ohms
You then have two different earthing systems in close proximity. The gland or end of The cable should be placed within an all insulated enclosure.
 
Tt is gland swa onto paxolin plate then bolt to base of dB and run earth straight from dB usaly 1 rod will get you around 30-40 ohms

That creates a dangerous situation because you have metal connected to two different earthing systems exposed inside the DB.

1 rod? How long, what material, what type of soil, whereabouts in the country, will that be ok for the available fault current?
 

Reply to 3 phase supply to classroom, unsure to TT? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
712
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top