O
Outspoken
Lol, .....This sounds as though you are rewriting 559.6.2.3 and you claim to have NICIEC, NAPIT, ELECSA with even the IET agreeing with you?
Maybe the IET made a mistake?.......Lol.
I have re-written nothing and it was after reading that I decided to contact the relevant organisations to get clarity. I'll admit that each one interpreted the "common neutral" in a slightly different way, and I would question if the NAPIT chap I spoke to understood the difference between common neutral and borrowed neutral, however I believe he actually meant the same thing as the others but was poor at explaining that.
I believe, based on the conversation had with the IET that the regulation is meant to be interpreted as each line of lights from a phase would have it's own neutral, but as these would be contactor controlled the neutrals would return to the output side of the contactor, thus making them common, but not borrowed between the phases as would be the case if looped across the phases. The contactor in turn would be protected on the load side by a TP+N MCB and a single phase supply (Taken from one phase) for the coil.
Now that is no different to what I believe the majority of us have done over the years and is in perfect agreement with 559.6.2.3 and I believe (please correct if wrong Mr Skelton) that this is what D.Skelton actually meant in his posts too
Now if you want to interpret the regulation to mean you can use a common neutral and a TP+N on three lighting circuits across phases with the neutral looped and no contactor then good luck to you, but I do believe you would be interpreting it incorrectly and may be criticised during an inspection for this.