If your talking about 3 phase bus bar type affairs with plug-in connections
This (and other similar types of set up) is exactly what we are reffering to.
You can rest easy Eng!
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 3 sp circuits off a tp isolator in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
If your talking about 3 phase bus bar type affairs with plug-in connections
As i have said before i said a carefully designed set-up with added monitoring or pre-designed system like track lighting, we all seem to be arguing the same side of the coin from a different angle its just the case that its not the most common method in most members experience hence it throws up a lot of interest if ever mentioned and yes 4pole devices if they could fit your board as long as it early make / late break on the n cos we wouldn't want to be zapping the lighting with a voltage spike as you star point the N by accident.If your talking about 3 phase bus bar type affairs with plug-in connections, then fine your never going to loose the neutral along it's length are you. But conventional lighting wiring methods no way, that neutral single conductor can end up three times the length of the phase conductors if wired in banks per phase!! Breaks in that single neutral conductor could add more than a little interest too!! Now why would you not run a separate neutral conductor with each phase leg, and if you are going to use a 3 pole breaker why not a four pole, so that if fault did occur, the breaker would isolate ALL live conductors!!
I think everyone knows why it's a bad idea on three socket circuits, there are various reasons, however it's common practice on lighting circuits so that might be one of many reasons why there is nothing specific in the regs about it.
Just my thoughts?
Apologies for the confusion.I think everyone knows why it's a bad idea on three socket circuits, there are various reasons, however it's common practice on CERTAIN TYPES of lighting circuits so that might be one of many reasons why there is nothing specific in the regs about it.
I think everyone knows why it's a bad idea on three socket circuits, there are various reasons, however it's common practice on CERTAIN TYPES of lighting circuits so that might be one of many reasons why there is nothing specific in the regs about it.
When I refer to common practice I am only referring to the pre wired, modular trunking systems and busbar lighting track which are common in larger commercial installations. I agree and when I have installed these they have always been contactor controlled, I wouldn't do it any other way. With regards to wiring standard lighting circuits in this way, I am fully aware that this is a big no-no. I should have made it clearer and said something like this: Apologies for the confusion.
As i have said before i said a carefully designed set-up with added monitoring or pre-designed system like track lighting, we all seem to be arguing the same side of the coin from a different angle its just the case that its not the most common method in most members experience hence it throws up a lot of interest if ever mentioned and yes 4pole devices if they could fit your board as long as it early make / late break on the n cos we wouldn't want to be zapping the lighting with a voltage spike as you star point the N by accident.
We will have to agree to disagree on that but I hold your position to be questionable.
Running three single phase lighting circuits in one location to load spread is indeed common practice, but the only time they should be on a common 3P+N MCB/Isolator etc is when contractor controlled so they are effectively a 3 phase circuit and should be treated as such. Neutrals should not be looped though and may come back to a common point but should be separate for each on the lighting legs.
If you are talking about standard lighting circuits with conventional switching etc then they should be on separate MCB's and not a 3 pole. They should not have shared neutrals and to do so would be extremely bad in my humble opinion.
Oh by the way, just got off the Phone with the NICEIC who agree with me on this, as do NAPIT and ELECSA. I have also conferred with the IET who have condemned the notion of running single phase circuits, except as stated where controlled via a contactor, via a 3 pole MCB/Isolator whether the neutral is shared or not.
I will admit that no-one could specifically point to a regulation to prevent someone doing this, but all stated they would not consider this good practice or good design.
Reply to 3 sp circuits off a tp isolator in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net