If your talking about 3 phase bus bar type affairs with plug-in connections, then fine your never going to loose the neutral along it's length are you. But conventional lighting wiring methods no way, that neutral single conductor can end up three times the length of the phase conductors if wired in banks per phase!! Breaks in that single neutral conductor could add more than a little interest too!! Now why would you not run a separate neutral conductor with each phase leg, and if you are going to use a 3 pole breaker why not a four pole, so that if fault did occur, the breaker would isolate ALL live conductors!!
As i have said before i said a carefully designed set-up with added monitoring or pre-designed system like track lighting, we all seem to be arguing the same side of the coin from a different angle its just the case that its not the most common method in most members experience hence it throws up a lot of interest if ever mentioned and yes 4pole devices if they could fit your board as long as it early make / late break on the n cos we wouldn't want to be zapping the lighting with a voltage spike as you star point the N by accident. ;)
 
I did try and offer that calc as a way of calculating neutral currents earlier. We have raised this formula before, and I proved through a power analyser (screen shots I posted) that it doesn't work where harmonics are involved.

however in the instance I used, the harmonics were large enough that an active filter was used. The OP discussed sockets, in which only a crystal ball can predict future usage.
 
A couple of weeks back 4 transformers failed in Nottingham, from what I can gather it was the neutrals that failed. I live in student land so lots of SMPS’s. It’s a wonder the leccy board don’t put a zip fastener along the cable runs. No sooner have they filled one hole in their digging another, neutrals failing.

The neutrals in Victoria Centre are near melting! It’s only going to get worse. The transformers taking the brunt of it as they are the main filter for harmonics.
 
I think everyone knows why it's a bad idea on three socket circuits, there are various reasons, however it's common practice on lighting circuits so that might be one of many reasons why there is nothing specific in the regs about it.

Just my thoughts?

We will have to agree to disagree on that but I hold your position to be questionable.

Running three single phase lighting circuits in one location to load spread is indeed common practice, but the only time they should be on a common 3P+N MCB/Isolator etc is when contractor controlled so they are effectively a 3 phase circuit and should be treated as such. Neutrals should not be looped though and may come back to a common point but should be separate for each on the lighting legs.

If you are talking about standard lighting circuits with conventional switching etc then they should be on separate MCB's and not a 3 pole. They should not have shared neutrals and to do so would be extremely bad in my humble opinion.

Oh by the way, just got off the Phone with the NICEIC who agree with me on this, as do NAPIT and ELECSA. I have also conferred with the IET who have condemned the notion of running single phase circuits, except as stated where controlled via a contactor, via a 3 pole MCB/Isolator whether the neutral is shared or not.

I will admit that no-one could specifically point to a regulation to prevent someone doing this, but all stated they would not consider this good practice or good design.
 
When I refer to common practice I am only referring to the pre wired, modular trunking systems and busbar lighting track which are common in larger commercial installations. I agree and when I have installed these they have always been contactor controlled, I wouldn't do it any other way. With regards to wiring standard lighting circuits in this way, I am fully aware that this is a big no-no. I should have made it clearer and said something like this:
I think everyone knows why it's a bad idea on three socket circuits, there are various reasons, however it's common practice on CERTAIN TYPES of lighting circuits so that might be one of many reasons why there is nothing specific in the regs about it.
Apologies for the confusion.
 
When I refer to common practice I am only referring to the pre wired, modular trunking systems and busbar lighting track which are common in larger commercial installations. I agree and when I have installed these they have always been contactor controlled, I wouldn't do it any other way.

With regards to wiring standard lighting circuits in this way, I am fully aware that this is a big no-no. I should have made it clearer and said something like this:

I think everyone knows why it's a bad idea on three socket circuits, there are various reasons, however it's common practice on CERTAIN TYPES of lighting circuits so that might be one of many reasons why there is nothing specific in the regs about it.

Apologies for the confusion.
 
When I refer to common practice I am only referring to the pre wired, modular trunking systems and busbar lighting track which are common in larger commercial installations. I agree and when I have installed these they have always been contactor controlled, I wouldn't do it any other way. With regards to wiring standard lighting circuits in this way, I am fully aware that this is a big no-no. I should have made it clearer and said something like this: Apologies for the confusion.

Well that's cleared that one up then...!! lol

To be honest, i was more than a little surprised you were in favour of installing such a system, while the confusion was still reigning!!

I have seen such systems in use, and seen the consequences when things go wrong too!! It was on a NEC spec'd project and can still see clearly in my mind how the single neutral was branched off to supply light fittings. ....Yep you guessed it WING NUTS!! A good 30 or so of them!!

Haven't seen that guy about much here lately, that reckoned the Yanks multi branch circuits for both sockets and lighting, were going to be the way of the future in the UK!! He really was a classic with some of his ideas!! lol!!
 
As i have said before i said a carefully designed set-up with added monitoring or pre-designed system like track lighting, we all seem to be arguing the same side of the coin from a different angle its just the case that its not the most common method in most members experience hence it throws up a lot of interest if ever mentioned and yes 4pole devices if they could fit your board as long as it early make / late break on the n cos we wouldn't want to be zapping the lighting with a voltage spike as you star point the N by accident. ;)

As far as i'm aware, most 2 and 4 pole breakers, (certainly those supplied to us by Schneider (MG)) have a designated Neutral pole for that very reason.
 
Don’t know about the smaller MG breakers, but the larger MCCB’s and ACB’s you can specify simultaneous break. I had to use these for high current double pole single phase supplies, up to 4000A where we doubled up the poles in a 4 pole unit.

Check the specification and you’re requirements first.
 
We will have to agree to disagree on that but I hold your position to be questionable.

Running three single phase lighting circuits in one location to load spread is indeed common practice, but the only time they should be on a common 3P+N MCB/Isolator etc is when contractor controlled so they are effectively a 3 phase circuit and should be treated as such. Neutrals should not be looped though and may come back to a common point but should be separate for each on the lighting legs.

If you are talking about standard lighting circuits with conventional switching etc then they should be on separate MCB's and not a 3 pole. They should not have shared neutrals and to do so would be extremely bad in my humble opinion.

Oh by the way, just got off the Phone with the NICEIC who agree with me on this, as do NAPIT and ELECSA. I have also conferred with the IET who have condemned the notion of running single phase circuits, except as stated where controlled via a contactor, via a 3 pole MCB/Isolator whether the neutral is shared or not.

I will admit that no-one could specifically point to a regulation to prevent someone doing this, but all stated they would not consider this good practice or good design.

Lol, .....This sounds as though you are rewriting 559.6.2.3 and you claim to have NICIEC, NAPIT, ELECSA with even the IET agreeing with you?

Maybe the IET made a mistake?.......Lol.
 
In my experience, those who shout loudest normally have the least to say.
 
No matter what, supplying/wireing 3 single phase circuits via a 3 pole breaker with a single neutral conductor is not a very good idea at all. As far as i'm aware, only the Yanks and maybe, the now very few countries that have based their codes on NEC would use such a system...
 

Reply to 3 sp circuits off a tp isolator in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
597
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
774
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

If any appliance has a filter or surge protection device, you will have a device that can pass a small current between the L and E or the N and E...
Replies
1
Views
1K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top