I've been asked to price 3 X 7kw showers. There is a three phase board about 40 meters away. Can anyone see an issue with 40 amp three phase MCB with 10mm four core swa to a sub board then 3 X 32 amp rcbos for each individual shower.

Cheers
 
Pre made units that can limit the amount of current drawn by only letting one shower be energised at a time.

For clarity, I'm not saying one needs to be used, but was asking if one was being used as I've never fitted one and would be interested if one was.
As would I, as would I.
 
I thought that in a three phase supply that if you have 32 amp running on each phase then they would be balanced and you would have nothing down the neutral?
They don’t balance out over the single phase part.
They only balance out over the 3 phase part, once the 3 neutrals are connected together.
Even then, they only actually balance if all the phases have the same loading at the same time.
As a rule of thumb, double the single phase load to determine the CSA of the neutral for the 3 phase part.
So if each phase will be feeding a 7kw shower, that makes 14kw.
 
Last edited by a moderator:
They don’t balance out over the single phase part.
They only balance out over the 3 phase part, once the 3 neutrals are connected together.
Even then, they only actually balance if all the phases have the same loading at the same time.
As a rule of thumb, double the single phase load to determine the CSA of the neutral for the 3 phase part.
So if each phase will be feeding a 7kw shower, that makes 14kw.


So why on a 100amp supply do we have 25mm tails and neutral?
 
They don’t balance out over the single phase part.
They only balance out over the 3 phase part, once the 3 neutrals are connected together.
Even then, they only actually balance if all the phases have the same loading at the same time.
As a rule of thumb, double the single phase load to determine the CSA of the neutral for the 3 phase part.
So if each phase will be feeding a 7kw shower, that makes 14kw.


Yes so the neutrals will be connected at the sub board?
 

Reply to 3 X single phase showers in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top