I've been asked to price 3 X 7kw showers. There is a three phase board about 40 meters away. Can anyone see an issue with 40 amp three phase MCB with 10mm four core swa to a sub board then 3 X 32 amp rcbos for each individual shower.

Cheers
 
I'm guessing you can't get RCBO's for whatever board you have already installed, can't see any problem but what are you going to do with the spare ways? , might they get used for something else in the future? and take the total load up past the 40 amp MCB?
 
Hi - if I understand correctly you plan to have one shower per phase to spread the load. This means you will need L and N for each shower (i.e. each 10mm L needs its own 10mm N).
The triple-pole is a submain to another board for the showers.
 
I've been asked to price 3 X 7kw showers. There is a three phase board about 40 meters away. Can anyone see an issue with 40 amp three phase MCB with 10mm four core swa to a sub board then 3 X 32 amp rcbos for each individual shower.

Cheers
Yes, I’m thinking 16mm2.
 
What is a "shower priority contactor"?

Pre made units that can limit the amount of current drawn by only letting one shower be energised at a time.

For clarity, I'm not saying one needs to be used, but was asking if one was being used as I've never fitted one and would be interested if one was.
 
Pre made units that can limit the amount of current drawn by only letting one shower be energised at a time.

For clarity, I'm not saying one needs to be used, but was asking if one was being used as I've never fitted one and would be interested if one was.
As would I, as would I.
 
I thought that in a three phase supply that if you have 32 amp running on each phase then they would be balanced and you would have nothing down the neutral?
They don’t balance out over the single phase part.
They only balance out over the 3 phase part, once the 3 neutrals are connected together.
Even then, they only actually balance if all the phases have the same loading at the same time.
As a rule of thumb, double the single phase load to determine the CSA of the neutral for the 3 phase part.
So if each phase will be feeding a 7kw shower, that makes 14kw.
 
Last edited by a moderator:
They don’t balance out over the single phase part.
They only balance out over the 3 phase part, once the 3 neutrals are connected together.
Even then, they only actually balance if all the phases have the same loading at the same time.
As a rule of thumb, double the single phase load to determine the CSA of the neutral for the 3 phase part.
So if each phase will be feeding a 7kw shower, that makes 14kw.


So why on a 100amp supply do we have 25mm tails and neutral?
 
They don’t balance out over the single phase part.
They only balance out over the 3 phase part, once the 3 neutrals are connected together.
Even then, they only actually balance if all the phases have the same loading at the same time.
As a rule of thumb, double the single phase load to determine the CSA of the neutral for the 3 phase part.
So if each phase will be feeding a 7kw shower, that makes 14kw.


Yes so the neutrals will be connected at the sub board?
 
If, you’ve stopped posting for a bit, I’ll try to explain.
25mm2 is over sized for 100A to allow for imbalances.
The outgoing circuits from the 3 phase board may all be single phase, 3phase or a mixture of both.
The conductors for each outgoing circuit should be sized appropriately.
When the neutral current from phase L1 gets back to the board, it can now use the L2 neutral conductor to flow to the L2 phase, and the neutral current from the L2 phase can use the L3 neutral conductor to flow to the L3 phase, etc.

So once the neutral currents get back to a single point, they can then start to balance themselves out.

In the OP’s situation, there is a very good chance that the 3 showers will not be used at the same time.
However there is a chance that 2 will be used at the same time.
If only 1 or 2 are used, the neutral currents will not be able to balance out.
If all 3 are used at the same time, they will balance out.
As such you need to size the neutral conductor to handle up to 2 lots of current.
 
Picking up the big hint from @westward10 - I had a go at a phasor diagram. If phase 1 shower is on, I get 30A (say) on the distribution circuit N. If phase 1,2 and 3 showers are all on then I get 0A on N, as they all cancel out. No big surprise as it's a balanced 3 phase load at that point. So what about when 2 showers are on? Hint - I was wrong before in #14 - it's my brain that's been flogged :) .
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester

Thread Information

Title
3 X single phase showers
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
67
Unsolved
--

Advert

Thread statistics

Created
David Rann,
Last reply from
bailes1992,
Replies
67
Views
7,808

Advert

Back
Top