Hi Fellow Sparks. I have to install a 30 metre run of Main Protective Bonding Conductor to Gas Main and Water Main in a commercial building. Is it permissible under the IEE Regs to clip a single 10 sq.mm PVC cable directly to the building surface for this, or should it be enclosed? Also, is it permitted to use one conductor for both Gas and Water as long as the first termination is unbroken at the earth clip? Cheers - Les
 
Last edited:
As long as no protection is needed against vandals, or vermin or cars etc I can`t see a problem ( though it does`nt always look very pretty)
 
What about protection against Pikies nicking it :shocked3:

James always the optimist.
You do what’s right for the situation, but who knows what will happen in the future.
We plan for today and with a bit of thought for the future.
Pikies aren’t on my spreadsheet!
 
Last edited by a moderator:
Hi Les, I'm surprised that nobody else has spotted a major flaw in your plan, namely that the maximum length of 10mm[SUP]2[/SUP] cable you can run and still achieve a maximum bonding conductor resistance of 0.05 Ohms is 27m, therefore you will need to run 16mm[SUP]2[/SUP] (43m Max) to achieve compliance with BS7671.
 
Last edited by a moderator:
I like to also know the reg that says a bonding conductor as to be ≤ 0.05 ohms ..................... I always felt that this was a guide, and though a good one not set in stone.

If the building is metal framed then could you not utilize the framework as your bonding conductor.
 
Last edited:
No such thing as 0.05

We were working on a large installation a while back and there was no bonding in place. After calculating the csa of the armourings ect found the tn-s install would require bonding conductors 120mm ect as they were so far from the origin and the resistance loss in the swa. We were concerned about this and phoned the IET technical helpline. The gentleman on the phone infomed us that they do not know where this <0.05 ohm came from . He informed us that as it states in the regs the maximum size of a bonding conductor for tn-s is as stated 25mm2
 
is not the 0.05ohms the figure we should get between bonded extraneous pars, e.g. gas and water pipes?
 

Reply to 30 metre run of Main Protective Bonding Conductor to Gas Main and Water Main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top