32a mcb on a 2.5m radial | on ElectriciansForums

Discuss 32a mcb on a 2.5m radial in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Iona222

Trainee
Joined
Mar 11, 2021
Messages
184
Reaction score
41
Location
London
Is the above OK, its feeding a fused spur downstream with a combi boiler attached to the spur. Cheers
 
Radial or spur?

Radial no
Spur yes (but not recommended as someone may convert to a Radial - it would be an easy error)
 
As I said its a 32amp mcb, feeding a fused spur downstream. Connected to a combi boiler, obviously the reason I'm asking as I think its to high, im going to change it to a 20 amp. Cheers.
 
433.1.204 Accessories to BS 1363 may be supplied through a ring final circuit, with or without unfused spurs,
protected by a 30 A or 32 A protective device complying with BS 88 series, BS 3036, BS EN 60898, BS EN 60947-2 or BS EN 61009-1 (RCBO). The circuit shall be wired with copper conductors having line and neutral conductors with a minimum cross-sectional area of 2.5 mm2 except for two-core mineral insulated cables complying with BS EN 60702-1, for which the minimum cross-sectional area is 1.5 mm2. Such circuits are deemed to meet the requirements of Regulation 433.1.1 if the current-carrying capacity (Iz) of the cable is not less than 20 A and if, under the intended conditions of use, the load current in any part of the circuit is unlikely to exceed for long periods the current-carrying capacity (Iz) of the cable.
 
If it is a spur from a ring, even if it is spurred off from the origin, then it is ok
 
As I said its a 32amp mcb, feeding a fused spur downstream. Connected to a combi boiler, obviously the reason I'm asking as I think its to high, im going to change it to a 20 amp. Cheers.
So the overload protection is downstream of the cable. It will prevent an overload.

The 32A device will provide fault protection for the cable.

The arrangement is fine.

But totally pointless. Change it to a 20A if you want. Will need testing and certifying.
 
Even though it's fine I'd agree with downrating the breaker simply to save arguments and reduce confusion in future. It will instantly look suspicious in an inspection as it stands.
 

Reply to 32a mcb on a 2.5m radial in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thank you everyone for your comments Celia
Replies
6
Views
700
Yes… as long as the initial radial circuit is designed properly regarding OCPD, cable size and rcd protection.
Replies
1
Views
833

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top