Just wanted to see if I'm being a bit too 'picky' but I've come across a few installations recently which have a 32A mcb for a radial circuit using only 2.5mm cable for which the current carrying capacity is approx 26A. I've been picking it up but it seems to be quite common. What do others do in these situations
 
AS chris has said 32amp for a ring 20 / 16 amp for a radial 2.5 is rated at 26 amps clipped direct so when protected by a 32 amp mcb its 6 amps more than carrying current capacity , and if its a rewireable fuse 3036 , even more as you have a correction factor of .725 to add to the equasion , and also if you have insulation covering it not exceeding 100 mm method 100 ,its rated at 21 amps more than 100mm its rated at 17 amps method 101 so max mcb rating would be 16 amps ,in my view your not being picky you are being correct so ,coding its a risk of overload so Code 1 it
 
Last edited by a moderator:
Cheers for the replies guys it confirms I was being correct its just that I've come across this so often recently it makes you wonder
 
yep alover the place especially in rewireable boards 3036 say 30 amp fuse 3036 / 0.725 = 41.37 amps

in the case of other factors that may be required : In / Ca x Cg x Ci x .725 = Amps

Correction factors :
Ca ambiant temperature
Cg Grouping
Ci surrounded by thermal insulation
0.725 correction factor for BS3036 rewireable fuses
 
Im not convinced its a code 1, as it doesnt present an immediate danger.

What about spurs?

Edit: Once again i didnt read the op properly. Been a looooooooong day. :D
 
It could if you stick large loads on it , understand what your saying about spurs but these normally are short lengths,however from the CDU it could be right through the loft and have more than one socket on it , when i do a PIR if i find these i test them indipendantly and some time you can have anything up to 10 sockets on it hence my reason for Code 1, jason i know how you feel get a beer and stick you feet up
 
Last edited by a moderator:
did a cu change the other day and found the immersion heater on a 30 amp rewirable with a 2.5mm cable. cable in conduit in a brick wall (equivalent derating of method B (if that is conduit on a wall) I believe, memory fades as the night wears on).

was tempted to put the new mcb in as a 32A.

the load (based on kw rating of immersion elements and other 'stuff' being fed from the circuit was around 20A.

good IR and very short run so low R1+R2 on the cable. about 15years old installation.

what would you guys have installed as a breaker?
 
If the 2.5 supplies a fixed load less than the CCC of the cable, then the 32 amp breaker is providing short-circuit protection only (and obv. earth fault). If it can be shown by calculation that this breaker will operate under short circuit conditions in a time sufficient that the conductors will not rise above their final limiting temperature (from their normal operating temp.) then the circuit complies with BS 7671 and is safe.
 

Reply to 32A mcb on a 2.5mm cable in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
480
  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
656

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top