I note that in answer to another EV Charger question a member suggested a 40A breaker would be preferred to a 32A because of many hours at continuous full 7kW load. I am not an electrician but understand the reasoning.
I have a 7kW charger (which generally runs full load for a continuous 5 hours during the off-peak period) and note that the electrician has connected to a 32A type B breaker in the CU and issued his NICEIC Domestic Electrical Installation Certificate accordingly. The circuit conductors are noted as 6mm csa
I have not experienced any problem with the installation but would the general recommendation be to increase the breaker to 40A?

Thank you.
 
Well, taking a look at BS 7671:2018 seems that for PVC , with Methods A,B,C ranges go from 32 to 47 A. Of course an isolated cable supports more , I think that in your country with less temperature and some more humidity and with your mass systems it could also work for 40 A, but as said, keep it up in 32 A for 6 mm2.
 
Surely this can be considered to be a fixed load, or at least a fixed maximum load of 32A.
Unfortunately not.

It's for an EVCP which is basically a fancy socket outlet.

The EVCP tells the vehicle that it has a maximum current of 32A.

The charger within the vehicle then (if working correctly) will charge at the 32A rate - or a reduced current if the in-vehicle charger has a maximum of say 28A.

However there is nothing inherently limiting this current, if the in-vehicle charger goes faulty, it could take much more than it should.


A fixed load is only where it is not possible to take more than rated as an overload, other than for fault type conditions.

An immersion heater for example is limited by its internal resistance, it wouldn't be able to overload, only suffer a fault.
 
An immersion heater for example is limited by its internal resistance, it wouldn't be able to overload, only suffer a fault.
I won't mention the one I came across once, then. The outer sheath of the element had dissolved and the element spiral had shorted to the sheath part way along. It enjoyed a significant, but brief life, as a 6kW immersion, before failing completely. No RCD in the circuit, of course, and TNC-S (or PME as it was then.)
 

Reply to 32A or 40A breaker for 7kW EV Charger in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
707
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Thank you everyone for your comments Celia
Replies
6
Views
794
  • Question
Agreed, loss of N further down the network can give wildly changeable voltages If it is tied to earth, then that will go up and down too.
Replies
3
Views
411

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top