Hi we have a client who insists on using 3kw induction hobs on their projects. These hobs are used 8-10hours per day and come with a moulded plug top. Safe to say the socket outlets keep melting/burning out. First thought was to remove the plug top and wire via a 16amp commando and appropriate 16amp rcbo (These sockets are wired on their own dedicated radial one radial per socket.) However removing the plug top would invalidate the warranty. The appliance is wired with a 1.5mm rubber flex. Not sure what else we can do with this other than tell the client to buy induction hobs that comes with a 16amp commando in the first instant. What's your thoughts on this? Thanks in advance.