Have you checked delta contactor? Could be a phase down
 
You have removed the links when you connected the motor to the star delta contactor?
 
Hi yes we was testing separate items out of stores. So not knowing conditions of either item.
Motor was original connected to dol and ran fine.
Obliviosly links were took out to connect to 6 wire star delta.
Thinking must be delta contactor problem.
But just curious now as someone mentioned not all 6 wire motors will run on. Motor reminders confirm motor will run in either.
Anyway items been put back on shelf for another rainy day tidy up.
Thanks for everyone's help.
 
Hi yes we was testing separate items out of stores. So not knowing conditions of either item.
Motor was original connected to dol and ran fine.
Obliviosly links were took out to connect to 6 wire star delta.
Thinking must be delta contactor problem.
But just curious now as someone mentioned not all 6 wire motors will run on. Motor reminders confirm motor will run in either.
Anyway items been put back on shelf for another rainy day tidy up.
Thanks for everyone's help.
Three phase squirrel cage motors will have 6 ends at the terminal block, it's how they are connected that determines how they start and run.
 
My money is it not being wired correctly.

When going into delta it's ending up running on 2 phases. Seen it dozens of times with people who don't have much experience with them.

If it runs fine in star then the motor is fine.
 
[ElectriciansForums.net] 3ph star delta starter motor drawing high amps

This is exactly the mistake I presume it to be, should have read the comments before responding.
 
This is exactly the mistake I presume it to be, should have read the comments before responding.
Using the Erroneous diagram , with K3 closed .
Are we looking at a form of symmetry forcing L1 and L3
into a tussle , and possible some circulating currents in the V1 & V2 contacts of K3 ?
Not Pretty !
(Spotted quite a few suspect /tweaked diagrams -Googling!)
 
As static zap said - The erroneous diagram in delta mode connects the U and W windings in parallel across L1 and L3 and shorts the V winding (and connects it to L2 only at one end but no current is drawn from L2). Acting as a three similar winding transformer and Lenz's Law, the alternating magnetic fluxes around each winding must be equal in magnitude and together sum to zero. Thus the currents in each winding are the same in magnitude. The OP sort of told us this in his first post - 'taking 38A on all' - the currents being 120 electrical degrees apart).
 
Last edited:

Reply to 3ph star delta starter motor drawing high amps in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
704
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top