This is one of a weekly question by sparks magazine posted on Facebook to win free tools each week. Everyone has answered B. 8Volts. I am not sure this is correct. Please could anyone help me with this. I have posted it up in here rather than just the trainee section so more people will see it. Not bothered about the prize. I just have a feeling that 8volts is wrong, but would happily be corrected on this.:) Thanks.

To comply with IEE Wiring Regulations the voltage drop on a three phase 400v Circuit should not exceed:
a) 4v
b) 8v
c) 20v
d) 32v
 
Look at the 3 phase waveforms...
When L1 is at V[SUB]pk[/SUB], L2 & L3 are at -0.5V[SUB]pk[/SUB]'

so... assuming 5% drop and balanced load,
vd on L1 is 0.05*sqrt(2)*230 = 16.3V
vd on L2/3 0.05*sqrt(2)*-230/2 = -8.13V

so total vd is 16.3 + (-8.13) = 8.13Volts.



Whether there's any truth in the above, I'll wait for higher beings to comment!!! :)
 
Look at the 3 phase waveforms...
When L1 is at V[SUB]pk[/SUB], L2 & L3 are at -0.5V[SUB]pk[/SUB]'

so... assuming 5% drop and balanced load,
vd on L1 is 0.05*sqrt(2)*230 = 16.3V
vd on L2/3 0.05*sqrt(2)*-230/2 = -8.13V

so total vd is 16.3 + (-8.13) = 8.13Volts.



Whether there's any truth in the above, I'll wait for higher beings to comment!!! :)


None what so ever :)
 
Look at the 3 phase waveforms...
When L1 is at V[SUB]pk[/SUB], L2 & L3 are at -0.5V[SUB]pk[/SUB]'

so... assuming 5% drop and balanced load,
vd on L1 is 0.05*sqrt(2)*230 = 16.3V
vd on L2/3 0.05*sqrt(2)*-230/2 = -8.13V

so total vd is 16.3 + (-8.13) = 8.13Volts.



Whether there's any truth in the above, I'll wait for higher beings to comment!!! :)

Definitely something i have not done at college. Very interesting though.
 
Look at the 3 phase waveforms...
When L1 is at V[SUB]pk[/SUB], L2 & L3 are at -0.5V[SUB]pk[/SUB]'

so... assuming 5% drop and balanced load,
vd on L1 is 0.05*sqrt(2)*230 = 16.3V
vd on L2/3 0.05*sqrt(2)*-230/2 = -8.13V

so total vd is 16.3 + (-8.13) = 8.13Volts.



Whether there's any truth in the above, I'll wait for higher beings to comment!!! :)

Just remember V = I x Z, so without I and Z there is no V

Cheers :)
 
I can see now said the blind man :)

Ive not seen that method Simon provided

Okay i used polar coordinates to arrive at my 15 amps at a angle of 60 degrees.

Reference L1 = 40, L2 =30 and L3 =20

So in rectangular form we have 15 + j8.66, if we Sqroot the rectangular form you get the magnitude 17.32 amps.

My phasor diagrams back this up, what happened to my earlier diagrams, dodgy ruler :)

Ill crawl back under my stone now.

Chris
 
Do what?!?!
Workings please! :)

No need for workings, people are looking way too much into this.

Imagine a TP+N board. On this board is one single balanced three phase load pulling 10A per phase, what is the current in the supply neutral? 0A right? Add a 5A single phase load onto that board, what is the current in the supply neutral then? 5A. This would be both the total, and the maximum amount of current in the neutral.

Add another 5A single phase load to a different phase as the first 5A load, the total neutral current is now 10A, but the maximum amount of current in the neutral at any one time is still 5A.
 
No need for workings, people are looking way too much into this.

Imagine a TP+N board. On this board is one single balanced three phase load pulling 10A per phase, what is the current in the supply neutral? 0A right? Add a 5A single phase load onto that board, what is the current in the supply neutral then? 5A. This would be both the total, and the maximum amount of current in the neutral.

Add another 5A single phase load to a different phase as the first 5A load, the total neutral current is now 10A, but the maximum amount of current in the neutral at any one time is still 5A.

The neutral current won't be 5 amps in your final scenario there.
 

Reply to 3phase volt drop. in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top