I have just installed 4 new split consumer units in an old edwarian house. The boards are not in the same place and are being fed by the meter in a barn about 60 meters away. Very unconventional setup. The tails (25mm) come into the kitchen and I have put the feeds for 3 of the boards through a 300ma rcd to protect the cable but this is making it impossible to test with my KT65 as it sometimes trips the 30ma rcd on the CU and sometimes the 300ma on the incomming board. Would I be better ommiting the 300ma rcd and just putting 100A incommers on ? The wiring is a mixture of 16 mm twin with a seperate earth (that seems ok) And the feed for the upstairs consumer unit is 16mm twin and earth (but has very little load. ) Hence the reason for the 300ma rcd in the main board. Obviously if that trips most of the house is in darkness so not good. I have told them that in my opinion it's much safer than the old fuses it had but obviously falls short of modern 17th regs. The small earth is an issue going to the upstairs. When I try a loop test with both rcds inline it just says no. (But I know it's intact) Other times it just trips the 300ma rcd (which I'm beginning to suspect is faulty). If I do the same test on a downstairs circuit it just gives me a correct reading (0.60 ohms which is ok considering the distances And 0.86 at the furthest socket) Replacing the cables is out of the question at the moment and I'm just trying to make it safe.
Anybody got a better sugestion ? I'm veering toward taking out the 300ma rcd ?
My first post so be gentle.
 
I admire you for tackling this. It is impossible for us to really comment on what you are up against, but from what you have described so far I think I would have offered 2 options regarding this setup.

1) New install to my design
2) Walk away.

Best of luck
 
One of the cables is a 2 core with a brass sheath used as a neutral.

Brass sheath?? Never seen or heard of such a cable system!!! Going purely on what you have written it sounds more like MICC, but illegally having the sheath used as the neutral conductor!! Almost like concentric wiring, but with a twist!! lol!! I would look into this cable configuration a lot deeper than you have, this sounds like a potential major cock-up waiting quietly to Bite!!!
 
The tails (4 in total ) are in swa. This part look like it was done by the distributor but why they put the meters in an out house god only knows. Like I said it looks like it has been there at least 30-40 years.
It has to be the most bizare set up around.
 
The brass sheath you spoke about does sound like pyro (micc) which if it is an the sheath is used as a neutral then that is a problem which needs addressing. Can you post a picture up of this cable? I assume this then has a separate cpc wired with it? Good luck. Sounds as though you'll need it. Personally I'd have insisted a full EICR be carried out prior to any work and then quoted accordingly. As said in a previous post, certain items would need upgrading to my design or I'd also walk away.
 

Reply to 4 consumer units in one house Help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
786
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
3K
  • Question
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2 3
Replies
31
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top