James Warren
I have just installed 4 new split consumer units in an old edwarian house. The boards are not in the same place and are being fed by the meter in a barn about 60 meters away. Very unconventional setup. The tails (25mm) come into the kitchen and I have put the feeds for 3 of the boards through a 300ma rcd to protect the cable but this is making it impossible to test with my KT65 as it sometimes trips the 30ma rcd on the CU and sometimes the 300ma on the incomming board. Would I be better ommiting the 300ma rcd and just putting 100A incommers on ? The wiring is a mixture of 16 mm twin with a seperate earth (that seems ok) And the feed for the upstairs consumer unit is 16mm twin and earth (but has very little load. ) Hence the reason for the 300ma rcd in the main board. Obviously if that trips most of the house is in darkness so not good. I have told them that in my opinion it's much safer than the old fuses it had but obviously falls short of modern 17th regs. The small earth is an issue going to the upstairs. When I try a loop test with both rcds inline it just says no. (But I know it's intact) Other times it just trips the 300ma rcd (which I'm beginning to suspect is faulty). If I do the same test on a downstairs circuit it just gives me a correct reading (0.60 ohms which is ok considering the distances And 0.86 at the furthest socket) Replacing the cables is out of the question at the moment and I'm just trying to make it safe.
Anybody got a better sugestion ? I'm veering toward taking out the 300ma rcd ?
My first post so be gentle.
Anybody got a better sugestion ? I'm veering toward taking out the 300ma rcd ?
My first post so be gentle.