The PSCC, on single phase is around 16,000amps, 3 phase 27,000amps.
That may be so. But my missus giving you the evil eye will guarantee to kill you faster and yet strangely more painfully.
as a follow up, in domestic breakers are rated at 6ka. in comerical/industrial mcbs are rated at 10ka.Where did you get those figures from?
For a fault of that magnitude you would have to be on the terminals of a 500KVA 11/.4KV transformer (4.5% impedance).
(Based on the infinite source method.)
Building supply:
There is a 415 volt supply into the building, 3 phases, 1 neutral and an earth. The 240v supply comes direct off one of the phases and feeds the sockets and lights. The other 2 phases are not used and end in the supply cupboard.
Hope that helps!
P.S. As for a quote, I have an electrician who I'm hoping can do the actual connecting to the board but I am just trying to save money on the thing I can do if possible. Thanks though!
i offered to quote him yesterday. this king of job is right up my street. been doing too much domestic lately. sick of seeing T/E that 's a pain in the arse when cold.
Can I ask what level of electrical experience you have.
mmm Tony, could it have been stressed (several times) in the past ? :biggrin:
Reply to the thread, titled "415v socket installation" which is posted in Commercial Electrical Advice on Electricians Forums.