The PSCC, on single phase is around 16,000amps, 3 phase 27,000amps.
That may be so. But my missus giving you the evil eye will guarantee to kill you faster and yet strangely more painfully.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 415v socket installation in the Commercial Electrical Advice area at ElectriciansForums.net
The PSCC, on single phase is around 16,000amps, 3 phase 27,000amps.
The PSCC, on single phase is around 16,000amps, 3 phase 27,000amps.
The PSCC, on single phase is around 16,000amps, 3 phase 27,000amps.
as a follow up, in domestic breakers are rated at 6ka. in comerical/industrial mcbs are rated at 10ka.Where did you get those figures from?
For a fault of that magnitude you would have to be on the terminals of a 500KVA 11/.4KV transformer (4.5% impedance).
(Based on the infinite source method.)
Building supply:
There is a 415 volt supply into the building, 3 phases, 1 neutral and an earth. The 240v supply comes direct off one of the phases and feeds the sockets and lights. The other 2 phases are not used and end in the supply cupboard.
Hope that helps!
P.S. As for a quote, I have an electrician who I'm hoping can do the actual connecting to the board but I am just trying to save money on the thing I can do if possible. Thanks though!
i offered to quote him yesterday. this king of job is right up my street. been doing too much domestic lately. sick of seeing T/E that 's a pain in the arse when cold.
as a follow up, in domestic breakers are rated at 6ka. in comerical/industrial mcbs are rated at 10ka.
Can I ask what level of electrical experience you have.
mmm Tony, could it have been stressed (several times) in the past ? :biggrin: