Steve93

-
Trainee
Joined
Apr 23, 2017
Messages
65
Reaction score
15
Location
Southampton
Eicr today had a 4mm T+E connected into the bottom of a main switch which went to a separate dB with 1 20amp rcbo. Then swa to a hot tub. That part is fine. What I’m unsure about is the reg I can say that the cables are not ok in the bottom of the main switch. The other dB is only about a ft away from the main one. What’s people’s thoughts on this? I know it’s rough as you like!!
 
[QUOTE - So the 4mm is protected by the cut out fuse?]

For fault current yep but depends on what type supply

[QUOTE So by the cut out fuse then?
What other ocpd is there?]

What over current can the 4mm suffer when it can pull no more than 20 amp?
 
[QUOTE - So the 4mm is protected by the cut out fuse?]

For fault current yep but depends on what type supply

[QUOTE So by the cut out fuse then?
What other ocpd is there?]

What over current can the 4mm suffer when it can pull no more than 20 amp?
Overload protection is not the issue,How about short circuit protection?
 
The problem is, you can't rely on the 20a rcbo to protect the 4mm. What I mean by this is, future alterations, who's to say someone won't split that 4mm and feed something another db etc. There is nothing to protect that 4mm from overload.

It's the same as having a 1.5mm t+e for a lighting circuit protected by a 45a but at fused down to 6a at the first luminaire.
 
A very poor installation but could be compliant if the connections are sound and the cable route to the 20A RCBO is suitable, then the RCBO can provide sufficient protection to be acceptable.
However there are a lot of caveats to the compliance so not generally a good idea.
[ElectriciansForums.net] 4mm cable into the bottom of main switch.
 

Reply to 4mm cable into the bottom of main switch. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957
  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top