32A ring main, adding 2 more sockets off this, spark I’m working with says add radial 4mm to 2 new sockets from ring I’m saying extend ring? I know 4mm can take 32A but I wouldn’t do it his way
 
I agree with you, I don't think it is a very good idea. I expect it'll be fine and you'll never have any problems but you could say that about a lot of electrical work that is poor.

If this 'radial' extension of the ring circuit is at a point near the consumer unit or rather the beginning of the ring, then in theory the cable from the CU to this point could end up carrying more current than it's CCC and the 32A MCB may not trip. This is pretty unlikely but possible.

Also appendix 15 BS7671 does state that an unfused spur from a ring should only feed one single/double socket, although I am not sure how Industrial relates to BS7671.

lastly, I guess your friend is doing this because it is 'slightly' easier than extending the ring. In the future someone else may add to these sockets with more 4mm, due to the fact it is there and easy to spur from. Just because your initial work may not really be dangerous I think it's good to look ahead and think how your actions may affect future decisions.
 
Last edited:
Non-compliant and would show up on an EICR.

I am not sure how Industrial relates to BS7671.
Same as any other installation. BS7671 covers everything from a flat to a nuclear power plant.
 
A heater is also mentioned, which will probably be at least 10A. The likelihood is that the total load would be maybe 10-15A which could result in a long, slight overload to the 13A FCU that will not blow the fuse. Although technically compliant, I would say this is bad practice for an industrial unit just to save a bit of cable. At our workshop two doubles would often get loaded to 30A total.
 

Reply to 4mm spurred from ring main in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
778
Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
335

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top