davesparks
Allowing a 2% vd you will scrape 80A on a 240. A 300mm will give you 90A.
I had a feeling 120 would be cutting it a bit close, my guess would be they are planning for a 63A circuit.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 5 core SWA 120mm pvc cable in the Commercial Electrical Advice area at ElectriciansForums.net
Allowing a 2% vd you will scrape 80A on a 240. A 300mm will give you 90A.
You would need 185 for 63A.I had a feeling 120 would be cutting it a bit close, my guess would be they are planning for a 63A circuit.
What size cable would he need to future proof for that?
Hi Buzz,Op should you not ne asking you spark that qestion.
Hello all
Thanks for your responses.
I believe that is 100 A total Split across three phases.
Client is talking to UK power networks about upgrading transformer to have 100 A from each phase.
What size cable would he need to future proof for that?
Thank you.
Thank you all for your responses, really appreciated. Regardless of the cable that will be finally specified I am still keen to know of the most cost effective electrical wholesalers from which to gain some prices any advice would be greatly appreciatedHe needs to decide what is happening with UKPN first before worrying about what size of cable to get.
But before that you need to know what size supply is actually required.
There's no point getting a bigger transformer installed if the current supply will do the job.
To get 100A over that distance I would hazard a guess at 2x 120mm in parallel, but that is just a guess.
Thank you all for your responses, really appreciated. Regardless of the cable that will be finally specified I am still keen to know of the most cost effective electrical wholesalers from which to gain some prices any advice would be greatly appreciated
No your right to be suspicious I am an electrical double agent that lurks on forums asking questions that only a non qualified lay person would ask?? I am putting the cable underground mate - only want to dig it and do it once!! got a big reel organised from a mate to help distribute the cable and don't like messing about that why i thought I would ask for help.Are we getting the full story here? Am I just being a bit suspicious?