Evening fella's, I'm doing a building tomorrow which contains 5 one bed flats, the building is number 1 on the street, would one EICR surfice, defects could be split into the different flats , or should I do 5 EICR's!
 
If each flat has it's own CU/DB then it's individual ones. If it's one covering the whole lot then one EICR should cover it.
 
Bit different but I've just done an office block, all one company. 4 floors each with own meter plus meter for landlord/communal. i did 5 individual reports.
 
If they have their own supply or split supply (service block after meter) they are considered as a separate installation and need their own eicr, if there are more than one cu but they are supplied from a cu on the same supply further up the system then you can use continuation sheets for the same eicr,

with a it's own supply you will have a different ze pfc and possibly tails, earth and bonding sizes and main switch, all which have their own condition report on the last few pages of the report


Loadsa paperwork!!!!
 
Building turned out to be 3 phase , 5 flats and a communal hallway, some flats had 2 CU 's because of the add ons, in total there was 11 CCU's! Covering the 6 reports that need doing, plenty of issues as you would expect.

I inspected 50% of all accessories, IR to earth all circuits in parallel, R2, ZS and RCD where required

Out of interest what would you charge
 

Reply to 5 flats....1 EICR?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

It won't be notifiable though as its not a new circuit, if you change the the tails from 16mm to 25mm is that notifiable? No, if you add an...
Replies
5
Views
452
Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top