Afternoon guys,
Just wondered what the difference is, if any between a 61009-1 RCBO and 61009-2 RCBO?
Are the characteristics different for any reason for different applications?
I noticed that 61009-2 came out 1995?
Thanks
 
According to BSi there is

BS EN 61009-2-1:1995 current
BS EN 61009-1:1995 withdrawn and replaced by ....
BS EN 61009-1:2004+A14:2012 current, but superceded

bit of a mess and I'm none the wiser
 
BSEN61009-1 are the general rules for household RCBOs
BSEN61009-2-1 is the applicability of the general rules to RCBOs functionally independent of line voltage.
BSIEC 1009-2-2 is the applicability of the general rules to RCBOs functionally dependent on line voltage.
 
BSEN61009-1 are the general rules for household RCBOs
BSEN61009-2-1 is the applicability of the general rules to RCBOs functionally independent of line voltage.
BSIEC 1009-2-2 is the applicability of the general rules to RCBOs functionally dependent on line voltage.
Thanks for information. I'm also wondering about automatic resetting RCBO's that are about. Are their any guide lines that governs there use, Anyone had any experience with these?
When I have time, I will have a look on Google. Thanks
 
Last edited:

Reply to 61009-1 or 61009-2 RCBO's in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Most instructions, including the one linked to earlier, ask for rcd protection… so that’s the answer in this particular instance. Whether regs...
2
Replies
15
Views
946
Adding a led strip isn't going to make much difference to the 3 phase balance. No real difference to where a 3 phase machine uses one phase to...
Replies
2
Views
386

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top