6mm Main Bonding on TN-S domestic install | Page 2 | on ElectriciansForums

Discuss 6mm Main Bonding on TN-S domestic install in the Domestic Electrician Forum area at ElectriciansForums.net

F

freedomrun

TN-S, 60A Main Fuse, 16mm Tails, 16mm Earth.

Question - CU change required & at the moment has 6mm Main Earth Bonding to gas & Water, less than 0.05 Ohms continuity measured & good condition. I'm pretty sure that this 6mm size Main bonding is compliant - just thought i would check if i should be aware of any other issue with leaving this in place. Thanks.
 
After a lot of research on this matter it has been drawn to my attention (via ECA and ESC) that minimum 6mm main bonding can stay in place on existing instalations providing they show no signs of damage and are verified adequate, and is left at your discretion but should be noted on the eic.

refered to reg 132.2 (or there abouts dont have regs handy)
ADDITIONS AND ALTERATIONS.
no alterations to properties unless EXISTING bonding and earthing are verified as adequate for the alteration.
 
Last edited by a moderator:
how would you do it?

check no signs of thermal (or mechanical) damage do continuity test on conductor, check adiabatic Ze, Zs etc then make an informed decision.

this is not a get out of upgrading bonding clause and in my humble opinion it should be carried out when possible.

Also a mention that pme supply must be pre 1988 if existing bonding is to be left in situ to comply with electrical safety regs.

Looked into this as firm i worked for were replacing load of social housing consumer units but didnt want bonding replaced unless needed so wanted something a little more concrete than "my boss told me to do it"
 
Last edited by a moderator:
Adiabatic is not applicable to bonding conductors.
and as ezzie says, use adiabatic to determine required size of main earth, then bonding needs to be not less than 50% of that. (TNC-S notwithstanding)
 
I actually mentioned DOMESTIC in my original post question as this is what the question was refering to.

On a Domestic TN-C-S with a 16mm bonding to the MET, my bonding to Gas and Water services must be 10mm if not mechanically protected?
 
Last edited by a moderator:
show/hideQ12. When carrying out electrical work on an installation forming part of a TN-C-S system, is it necessary to upgrade existing 6 mm² protective equipotential bonding to 10 mm²?

Not necessarily. If the existing 6 mm² bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not require to be upgraded.

Regulation number(s)
  • 132.16
  • 544.1.1
Just had similar problem ,researched into threads.The above para taken from the Electricity Saftey Council. Question and Answers page , Alterations.Would appreciate any ones take on this ??? hope there is no stoney silence!!!!!! i take it this refers to the main bonding
 
Last edited:

Reply to 6mm Main Bonding on TN-S domestic install in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
658
loz2754
L
A lot of external bonding or earth conductors are bare copper strips. If mechanical damage is likely, then run some steel conduit… but all UV...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top