Hello everybody, my name is Michael.

Last week a landlord called me regarding a faulty electric shower that the company tried to re fit under warranty but told him that the cable supplying it was under rated so they couldn't finish the job...

I went to take a look and the property being a hostel type flat in London did not meet 17th edition regulations. There was no RCD present and the consumer unit was older than me (27 years). I looked at the circuit supplying the shower and it was a 6mm twin and earth on a 50amp breaker. This obviously isn't correct as the run was over 15M and the shower was 9.5KW.

Obviously a shower pulling 38amps cannot be fed via a 6mm twin and earth on a 50amp breaker unless you were after an insurance job...

So after wrestling the metal cabinet off the Crabtree fuse board I noticed it was fed via a 6mm pyro. The circuits in the board were a cooker supply, upstairs lights, downstairs lights, immersion, upstairs sockets, downstairs sockets and a shower supply... Is the 6mm pyro capable of such demand?

I couldn't gain access to the meter cupboard to see what the fuse was feeding the flat, but to me it sounds a bit under rated?

The length of run is around 30M and the cable is clipped direct...

Obviously the landlord is asking me why it needs changing if 'its worked perfectly fine all this time'. But I don't really fancy putting my name on a job if I think it's going to be on the ITV headlines the next day.

Your views are welcome.

Michael > NICEIC registered > 10 years in the business
 
Yep pyro feeding the CU.

You reckon 57amps?

Its all pyro (I'm assuming).

I don't think a 4KW oven, 9.5KW shower and a immersion left on 24/7 is ideal on a 6mm pyro...

Whats the working life of pyro? I know it's good and has a long working life. All the circuits are wired in the stuff.

Also, the shower switch is recessed into the architrave with no back box...

^^^ just thought I'd share with you the amazing installations in London...oh and no earth sleeving or earth terminal behind the shower switch :)
 
There is a huge difference in the current carrying capacity of PVC twin and earth and pyro, you need to find out what feeds this shower.

Don't worry about the 6mm feeding the flat, half of London is the same :)

The working life of a pyro is double or triple that of PVC.
 
This topic isn't about the shower... I know how to sort that ;)

I just don't want to get involved in something that is going to cause me grief :/

Can pyro catch on fire? Will I have enough time to close my company and re open another in my imaginary wife's name?

michael
 
Why are you trying to replace something for the sake of it? Providing the fuse/breaker protecting the pyro is rated less than the current carrying capacity of the cable, what's the problem? What are the chances of the shower, immersion and oven all being on, full, at the same time?
 
WTF is this thread about again ?
so weve established a CU is fed by 6mm pyro thats rated for 57A.
so if the fuse backing that up is less than 57 then theres no prob.
and i find it puzzling that a spark of 10 yrs asks whether pyro will catch on fire lol.
 
I don't care about the pyro!! I care about blowing the incoming fuse and getting a call out because some polish girl is late for her cash in hand job.

It's a hostel...They don't pay for electricity...

The chances of ALL the appliances being on are high.

Ok, so say the pyro is fine. How the hell am I going to change the consumer unit when all the circuits are wired in old pyro! WHAT A HEAD ACHE.

Do I not bother about the existing consumer unit and just install a small RCD board feeding the shower?

I know how to get a round things, it was just the pyro I wasn't too keen on.
 

Reply to 6mm pyro... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
303
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
284
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
356

Similar threads

  • Question
Ouch. Danger notice to customer in my book.
    • Like
Replies
1
Views
597
  • Question
I went to look at a job like this a few years ago. My customer had a rental house, where there was an upstairs bedroom that had a newly built stud...
    • Informative
    • Like
2
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top