Hello everybody, my name is Michael.

Last week a landlord called me regarding a faulty electric shower that the company tried to re fit under warranty but told him that the cable supplying it was under rated so they couldn't finish the job...

I went to take a look and the property being a hostel type flat in London did not meet 17th edition regulations. There was no RCD present and the consumer unit was older than me (27 years). I looked at the circuit supplying the shower and it was a 6mm twin and earth on a 50amp breaker. This obviously isn't correct as the run was over 15M and the shower was 9.5KW.

Obviously a shower pulling 38amps cannot be fed via a 6mm twin and earth on a 50amp breaker unless you were after an insurance job...

So after wrestling the metal cabinet off the Crabtree fuse board I noticed it was fed via a 6mm pyro. The circuits in the board were a cooker supply, upstairs lights, downstairs lights, immersion, upstairs sockets, downstairs sockets and a shower supply... Is the 6mm pyro capable of such demand?

I couldn't gain access to the meter cupboard to see what the fuse was feeding the flat, but to me it sounds a bit under rated?

The length of run is around 30M and the cable is clipped direct...

Obviously the landlord is asking me why it needs changing if 'its worked perfectly fine all this time'. But I don't really fancy putting my name on a job if I think it's going to be on the ITV headlines the next day.

Your views are welcome.

Michael > NICEIC registered > 10 years in the business
 
I'm afraid i've had to use side cutters and long nose pliers on more than a few occasions in the past, it's no big deal really!! ....Unless you try to strip it like you would a PVC cable!! lol!!

That was the point I was making I could happily strip away with a pair of cutters and make an end off before others have set up their stripping tool and blunt blades. poaaibly mangling the sheath in the process

Using side cutters as you know has a knack to it
It can be a laugh a minute, watching someone try it who is not used to doing so
Those who have worked with pyro can also use the tools or improvise with whatever is at hand,the skill of the person can sometmes be judged when the cutters come out
 
I've never had to use pyro but I might buy a few meters to have a play with,
regarding E54s post I'm guessing your using the long nose pliers to open it, like youd open a tin of corned beef?

That's about the size of it Yes!! just don't use the short flimsy long nose pliers, mine are like a Mechanic's, with a nose about 6 to 7'' long. Always better to make your own emergency stripping bar whenever possible, it's a much easier and faster task then, especially if your terminating into a panel or CU etc... lol!!

Like many of the others here, that have extensive experience of working with MICC, i can terminate and make off the pot end without any of the specialised tools normally required/associated with terminating MICC... lol!!
 
I remember the first time as an apprentice making off my first pyro with the electrician watching closely. We had to make a stripping bar out of mild steel at college. having got the end started with the side cutters & then using the stripping bar (yes i did cut a foot or so off before stripping) I stripped it down to the required length & proceeded to screw on the pot by hand & then using footprints to tighten it fully,( & checking for that naughty little swarfe ring inside the pot & then blowing inside the pot to clear out the magnesium oxide powder that was when all hell let loose & made to look a complete idiot . oh well happy days.
 
As an aside copper itself tends to work harden over the years & getting the pots & seals as well as the glands for imperial sizes as used in the sixties in flats with concrete ceilings would be very difficult to get these days. If one of the conductors breaks of from the pot, whilst trying to manipulate it it becomes a real headache to deal with or if the outer sheath gets damaged the hygroscopic magnesium oxide will begin to absorb mosture & eventually will start to cause problems. Just not worth the hassell
 
You could always check this data sheet for conversion options for imperial pyro using metric seals

Don't know if they still do it but when Pyro was owned by BICC you could call the sales office and they would arrange for a pot to be drilled suit the imperial size you needed usually within 24 hours
 
You could always check this data sheet for conversion options for imperial pyro using metric seals

Don't know if they still do it but when Pyro was owned by BICC you could call the sales office and they would arrange for a pot to be drilled suit the imperial size you needed usually within 24 hours

Not heard of that for a long time now. Standard "conversion" now is a potted junction, and new cable from that to the termination. On fire anyhow, though on certain LV jobs, I've been asked to re-run the whole cable.

And yes others - the joys of pyro, or MICC - though what on earth MIMS is, is anyone's guess - Mummy's Insulated Milk System possibly?

As for the joys of wet pyro. Oh boy. Days (and nights) of fun! You very quickly learned to improvise on tools too - especially at 40 floors up from your main tool box.
 
Mineral Insulated Metal Sheath, the term is used to cover both copper and aluminium cables...

Well, now you put it like that.... I'd still far sooner work on Mummy's Insulated Milk System..... :)

Yes, it makes sense as such, I don't honestly think I've ever heard it described as such though - only as MICC or Pyro.

The aluminium is interesting - I thought we'd long done away with aluminium as a conductor for a number of reasons, and to my understanding, FP200 and similar cables which have an aluminium sheath don't qualify as MICC or MIMS...as they're not mineral insulated....

Time for me to do a little more reading up I think.
 
Well, now you put it like that.... I'd still far sooner work on Mummy's Insulated Milk System..... :)

Yes, it makes sense as such, I don't honestly think I've ever heard it described as such though - only as MICC or Pyro.

The aluminium is interesting - I thought we'd long done away with aluminium as a conductor for a number of reasons, and to my understanding, FP200 and similar cables which have an aluminium sheath don't qualify as MICC or MIMS...as they're not mineral insulated....

Time for me to do a little more reading up I think.

They made Pyro in both copper and alluminum, probably still do to some extent. I haven't seen it about for a number of years now though...

EDIT... You'll find that alluminium is still used as a conductor by the DNO's in virtually all of there distribution cables, including the bare overheads etc.... You'll also find a good deal of it in (multi-core distribution cables) being used in industry too...
 
Last edited by a moderator:

Reply to 6mm pyro... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
303
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
284
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
356

Similar threads

  • Question
Ouch. Danger notice to customer in my book.
    • Like
Replies
1
Views
597
  • Question
I went to look at a job like this a few years ago. My customer had a rental house, where there was an upstairs bedroom that had a newly built stud...
    • Informative
    • Like
2
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top