7.6kW Induction Hob - need to select cable and fuse size | on ElectriciansForums
Discuss 7.6kW Induction Hob - need to select cable and fuse size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
South West London
Hi everyone
I'm installing a Samsung induction hob - all 4 hobs total 7.6kW
Am I to apply diversity to this to work out the fuse size? I can imagine the 4 hobs being used at full throttle quite regular and don't want to put it on a 32A fuse and it keep tripping if I put it on a 32A fuse - what do you think?.
I was going to go with 10mm cable on a 40A fuse - can 6mm be used on a 40A fuse?
7.6kw? well allowing for diversity a 10mm2 cable will probably be way overkill unless your calculations you never posted up here say differently.
Well that's the whole point in my question. Why would you apply diversity when it's highly probable that all 4 hobs might be used at the same time on full throttle?
I have an induction hob, of around the same KW rating, and it's supplied by 6mm cable which also supplies my built in oven via a Dual connection unit. The RCBO protection at the CU is 32A...
All domestic cookers will be ok on a 32A mcb.
In any case 7.6kW @ 240V (which is what the manufacturer will state) is less than 32A.
Equal to 7.0kW @230V = 30.4A.
Just to be awkward, and taking on aboard all the above comment's, i would actually probably upgrade.
Yes, 99 times out of 100 every cooker will be more than adequate on a 32A breaker, but if there is the slight possibilty of it ever going over...id upgrade, it'll be just you're luck that the customer does have 4 on full throttle for ages and it trips then she trys to claim for the loss of more food than the house can take let alone the cooker.
As above, 7.6kW is just over 33amps....therefore the smallest possible chance of it overloading albeit VERY unlikley i still personally wouldn't risk it and would rather go overkill.
As above, yes at 230volts it would be below 32amps, and yes the manufactures do state it at 240, but as everyone well knows the supply is never at 230, always between 225 and as high as 250 at times.....
I can see the above points, that it would be overkill to upgrade and can understand why most electricians wouldn't as a 32amp breaker is pretty much more than adequate, but if you're wanting my opinion i would upgrade.
just fitted a fagor ind. hob about 8kw when talking to fagor about load was told it has 2 zones lh & rh each zone has a back ring and front ring , the temp adjustment is 0-9 however if if you set the back ring to 9 then turn the front to 9 the back ring will ramp down to 6 and visa versa so you cannot have all 4 rings on full, you can have a lh ring on full and a rh ring on full but the others will be on lower level
Anyone thought of using an amp meter to check what an induction hob 7.8 kw pulls at 230 v- 245v? and nobody has mentioned how the cable is installed ?
might be difficult to measure amps as the rings (or elements) seem to pulse when on so getting a true reading when all 4 are on would be a bit hit or miss
CTRL + Q to Enable/Disable FBPhotoZoom
Then you will be ripping-off your customer.
There isn't.
Then you don't undestand how they work.
No it isn't. See my previous post. It is correct.
The 230V values are what you should use for calculations.
There isn't a possibility.
If it complies with the regulations then overkill is just that and needless.
Then you don't understand.
An opinion is something to which you are entitled.
However, these are facts and you are wrong.
[/anger]
Reply to 7.6kW Induction Hob - need to select cable and fuse size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Thanks for the swift response.
N
He hasn't provided any certificates, including previous work. He sends invoices when he needs paying.but no vat registration number etc on...
  • Nessab16
  • Ireland
  • 8
  • 524
Nessab16
N