What's that got to do with anything? 7600 / 240 = 31.7 & 7000 / 230 = 30.4If we're going into basics....7.6 x 4.4 = 33.4
In what other circumstances do you dismiss the regulations?What you should use calculations for and what is reality isn't the same. Thats why the regs are non-stat.
If you want but you're still wrong.end.
What's wrong with everyone tonight?
The hob doesn't even come to 32A even if you work it out wrongly.
Nearly every cooker, including much larger, is on 6mm and 32A.
HOW MANY MORE TIMES?But for you to say that there is 100% no chance a 7.6kW cooker not tripping on a 32amp mcb is untrue.
All it takes is for the breaker to be soft and it probably would go.
Not actually blowing a fuse.Manufactures instructions aren't always true, have you never come across a 3kW immersion blowing a 13a fuse? because i have
What's that got to do with anything? 7600 / 240 = 31.7 & 7000 / 230 = 30.4
If you had even done that correctly you would have 7.6 x 4 = 30.4
In what other circumstances do you dismiss the regulations?
Are the regulations only for circumstances when you don't have a silly idea?
If you want but you're still wrong.
No Dave probably approx 6-8 metres all in to new oven placement when kitchen is fitted, but existing was 6mm into 45A switch then out to wall into an old BICC j.b. with 30A chocky block inside linking feed to old hob and old oven which was approx 4mtrs away in a unit so even then wasn't within 2mtrs of cooker switch ! I'm just trying to work out if I need to run a seperate 6mm to the new oven rather than existing 6mm to cover Induc hob & oven at total of 8.6kW ? As diversity on the oven inclusive of socket outlet incorporated in switch only drops it an amp or less. Running another 6mm would be a nightmare I reckon from CU.