H Chaps,

Can anyone tell me if the new regs require RCD protection for PVC conduit run to metal clad 20a DP switch? and also to a lighting circiut where the wiring is in minitrunking?

old dog learning new tricks (of the trade)

L
 
I didn't think so.

It's a small workshop with a 3 horse power table saw saw
The plan is to run 2.5 singles in conduit to the 20a switch for the saw; a 16a C type breaker should accommodate the start up induction current (around 15a and then run @ around 9a).
Lighting in conduit to wall plate level then in minitrunking to HF fluorescents, with non maintained emergency bulkhead on the phase.
RFC on 32a RCBO

Have I covered it?

That all looks fine Lionel.
 