also lets all remember we all use a nominal 230V to calculate Ampere, in reality most supplies are 240-249 V , which is 39.5A to 38.5 A, as Richard Burns says clamp it on start up when amps is highest, i have had 20 meters 2.5mm at 27A and no change in temperature, so 6mm will take at least 60A, make sure if cable goes in loft no insulation can be put over cable, and put a note in the consumer unit that must remain 40A cover your self. also do a Zs at the shower itself , i have had exactly same thing on a 5m run, so in theory passes but the Zs failed, so that means it had to be upgraded to 10mm.
does anyone else wonder why they don't do 8mm , seems most would find it useful in domestic. especially showers and ovens/hobs.