A 50mm earth should be pulled in alongside the swa. Alternatively If the water as stated above is the only extraneous part that needs bonding why not remove the metal pipes and install plastic. Are you sure theres no other parts that need bonding, structure or gas?
 
unfortunately there is 6 w.c units, 3 shower units and 3 kitchens all done in copper
so ive had various conversations with the design company (not that they say there wrong as such) but the regs say 50mm separate earth so thats what is going to be ordered
now an interesting question i have regarding the pme separate earth and possible long/ high currents within the earth if there is a fault on the neutral , is that in the main panel that has the 300mm feed tails , it goes into a 300ma rcd pri to feeding any outputs like the building that has the 95mm feeding

has that any relevance in this whole saga ??

thanks guys

knowledge is power and all that :)
 
I don't see the benefits of a 300ma rcd on a TN system, what type of site is it.
 
very strange site to be honest , theres the main offices we have just done , followed by an asbestos lab building then 2 x vehicle garages for there vehicles then a massive stores building and a scrap/ recycling plant at the far end with a few portacabin type units for something or other
 
unfortunately there is 6 w.c units, 3 shower units and 3 kitchens all done in copper
I know I'm a month late but you only need to insert an insulating section between the extraneous part and the part in the equipotential zone. Even a foot of speed fit pipe would be ample.
As long as it doesn't become extraneous elsewhere, it should test out fine once isolated from ground.
Having said that, I'm surprised a new building doesn't have blue mdpe incoming water.
 

Reply to the thread, titled "95mm 4core SWA, just trying to go definitive on the steel to copper calculation" which is posted in Commercial Electrical Advice on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top