Insulation resistance on 3phase board. Motors off at isolators. Main switch off, each circuit on. Mention to disconnect any electronics etc (digital power meter in this case). Later, on single phase board, no test from shower switch to shower. Also remember 2 way switching needs both strappers tested.
Ze, power is off. Disconnect main earth. Hang up plastic matts as a barrier to protect yourself. Ask for power on. Test ze. What would you do if ze a lot higher than stated? (tip- who's problem is it(external to installation!!)).
Rcd test, 15mA no trip, 30mA trip in 200ms, 150mA trip in 40ms.
Remember do both sides of sine.
Test button.
If an rcd is used on main board, 300ms is acceptable trip time. Good luck.