Just quoting for a C/U change, scenario is:-

O/S meter box, PME, existing 60A switch fuse in meter box, 16mm TWE from switch fuse to C/U in center of house with 16mm TWE coming down wall to C/U embedded in plaster, no bonding to water or gas.

Because the C/U is situated in center of house and all recently decorated it is virtually impossible to get anything new to it.


What i want to do is fit a 100A, 30mA, time delay RCD with 63A MCB in outside meter box.

Run 10mm G/Y to water and gas from meter box.

Change C/U.

I would love to upgrade the earth from meter box to new C/U but i don't think it is an option (obviously only 6.0mm earth in 16mm TWE).

Is this a "hanging offence" or do you think it is OK?
 
i would state on cert. as CU change only and try to upgrade the main earth. the T/E buried in the wall was done to previous regs and you're not obliged to RCD protect it.
 
he's saying that as the tails were installed previously you are not responsible for adding RCD protection.

God help us all if the clowns add this little gem to the next version of the regs.
 
state nothing out of the ordinary on the cert and write nothing in the deviations section.
there are no rules against using the t&e cpc for a submains so crack on.
and if you did adiabatic im sure it will say less than 4mm for the earth. ;-)
 
Had similar scenario last week which Biff kindly guided me on. The 6mm2 earth is fine if confirmed by the use of the adiabatic. However if you run new 10mm2 bonding to your internal consumer unit you must ensure the earthing is uprated to 10mm2 from the switch fuse. This would encompass a combined earthing and bonding conductor. Guidance notes 8 Earthing and Bonding will assist you with this.
 

Reply to A little help with the Reg's. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
454
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
833
  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
820

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top