Chr!s
-
With a Magnetic Ballasti It would be a 16 amp type C without further information. A 10 Amp type C would suffice for the one.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss A quick mcb calc for the newbies on here. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
With a Magnetic Ballasti It would be a 16 amp type C without further information. A 10 Amp type C would suffice for the one.
Chris ... it seems from your posts your looking to find the deeper aspect of the thread but i did express it was for newbies ...i want to see what the answers will be from their college teaching.. the point of the thread is to show them the reality of a stripped down education that leaves them out of their depth when venturing into commercial and industrial... with your post count and established members on your friends list i would assume this thread isn't aimed at you as you are trying to nit pick every angle ....
Not nit picking, just the way i was taught.
Its a standard high bay 400w high pressure sodium nothing different about it the bog standard version with a bog standard ballast and although you yourself haven't hit the intentional nail im trying to put forward on the head its clear your not fresh blood in the industry ...what further info do you need;
No im fresh blood, well in this game anyhow, thats why i answered
I given you the wattage, the lamp type expressed the run is nothing more than 20m and also said we can forget about cable calcs etc ...all i asked was what mcb and type to use on 1x 400w high pressure sodium ...
Well, the cable's do play a part in determing the MCB, especiallyl on large banks
College teaches you that its an inductive load and is subject to a 1.8 factor
So 400 x 1.8 =720w
college also teaches you an mcb with a type c rating should suffice for a inductive lighting load
so 720w/230v =3.13amps hence a 6amp type C should be ok
I have included the info of loses and control power too soo even with this
2.15amps x 1.8 = 3.87amps would still allow a 6amp type C to be acceptable
IS THIS THE CASE.. ?
the Clue is in the capital :wink_smile:
Its not the way i was taught.
Bring back the old 2360, (before even that got watered down!!) lol!! No multiple choice questions, an exam where you needed to KNOW and be able to explain the answers, or you failed!! ...lol!!
Bring back the old 2360, (before even that got watered down!!) lol!! No multiple choice questions, an exam where you needed to KNOW and be able to explain the answers, or you failed!! ...lol!!