A Rather Obvious Forged EICR

I know for a fact that the attached EICR is a forgery. I suspected as much even before I had been given a copy of the report.

My suspicions were confirmed the moment I noticed that the tester had entered 25 years as the estimated age of the installation. The installation is in fact, brand-new! The wiring was completed in July. The installation is within a newly-constructed, custom-built MOT testing station.

There is a story to be told about the events that took place prior to the EICR being issued which I will reveal in a later post. In the meantime, see how many irregularities you can find within this EICR.

I have redacted the report to spare any embarrassment for the company whose identity was stolen.
 

Attachments

I would say the block with the blue conductors at it looks like it shows signs of melting.

You are correct. I'm informed that prior to a 16mm SWA being installed to supply a sub-board for the office area, one of those twin and earths was acting as the supply cable! Apparently whoever installed the sub-board connected all the final circuits, but for reasons best known to himself, decided to spur the supply for the board from a ring final circuit elsewhere in the building. I don't know what he was thinking.
 
Why is there a smoke detector circuit on that type of installation unless it is a fire alarm,

There's a fire alarm panel, smoke alarms, call points and sounders present. I noticed that the panel is indicating a fault condition.

However, no certificate other than a MEIWC has been issued. Whoever did the work submitted a MEIWC to cover the design, installation and commissioning! There is no certification for the emergency lighting either.
 
Sounds like someone well and truly out of their depth.

That was my conclusion too. There is insufficient capacity in the main board. All the ways have been used. One of the breakers has three conductors. Two supply the main area lighting and emergency lighting. The other supplies one of the shuttered doors of which there are five in total. Another of the doors has been spurred direct from the ring final circuit.
 
I think the problem is an electrician can cover different levels of competence and you can always spot an electrician whos level of skill is domestic in a commercial world. Not that I am comparing one with another but there is one of those Nagey videos of him fitting SWA cables to a cable tray installed incorrectly and it looks appalling. A case of stick to what you know.
 
The Fault lies obviously with the idiot who contributed to the mess and the Builder enlisting a non licensed Electrician. The client should have requested his credentials prior to the commencement of work.

On Major sites in Aus. You have to provide an Electrical license and sometimes (A new thing appearing to stop things like this) a CV/Resume to check on your background to ensure you are capable.

I’m not knocking house bashers but Especially in Heavy Industrial and Mining they used to take them on as T/A’s (Mates)

---- work... terrible I’ve seen better in 3rd world countries.
 
Last edited:
Knowing your limitations as a sparks is equally as important as knowing what you can do...
Just the other day I was asked to quote for a job that requires a lot of reworking and installing new micc in a 1940s built chapel. I have declined as it’s beyond my level.
If it was one or two micc that need altering I ‘might’ have given it a go. But this job will require 40-50 alterations and additions all in micc.
Know your role
 
It’s been a long time since I worked on Pyro (MICC) the old sparks I worked with (Jurassic sparks) he bought me a set of MICC tools... Potting tool. Crimper and Stripper then took them away from me. I had to strip it with side cutters and a screwdriver. Use a set of pliers as a potting tool. His motto was do it the hard way and everything becomes easier. The same was with steel conduit. We used a block of wood with a slanted hole.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
JK-Electrical,
Last reply from
magnoliafan89,
Replies
56
Views
7,398

Advert

Back
Top