i was recently at a domestic job and just want to clarify something that happend, i carried out a periodic inspection and when i opend the single phase fuse board the main incomming neutral was lying disconected however the lights and all final circuits where functioning fine is this because the supply type is Tncs therefore the final circuits are gettin a neutral return via the earthing arrangments?any help would be appreciated