Guys just to clear up this post, i recently returned to the job and managed to find the fault by disconecting the main neutral from the supply authority isolater, and with the final circuits still functioning i disconected each neutral from the neutral bar 1 at a time untill they stopped working, so by proccess of elimination i found a neutral to earth fault in the lighting circuit, which ofcourse was supplying the full house with a neurtal link to earth. You would think simple enough to find haha however after inspecting every light there was no sign of neutral earth short, therefore the only place left that the fault could be is in 1 of 2 or the adaptiable joint boxes that for some reason was installed in the house during original installation!! which was coverd in artex and needed to be asbestos tested and the other behind the consumer unit haha so needless to say a nightmare job! however thanks for any help guys hope this helps with any faults in future