Found in many domestic installations, usually the only method of providing protection to tails in TT installations.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Absolutely no earth for lighting circuit. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Found in many domestic installations, usually the only method of providing protection to tails in TT installations.
Insulated and sheathed, is reinforced insulation.
Insulated and sheathed, is reinforced insulation.
Reinforced insulation is accepted as being double insulation.
Should be somewhere in the book.
I wonder why we bother writing these Regs, no one ever reads them.
412.1 Double or reinforced insulation is a protective measure in which:
(i) basic protection is provided by basic insulation and fault protection is provided by supplementary insulation, or
(ii) basic and fault protection are provided by reinforced insulation between live parts and accessible parts.
NOTE: This protective measure is intended to prevent the appearance of dangerous voltage on accessible parts of electrical equipment through a fault in the basic insulation.