I don't need to. It was the fact you mentioned there is water between cores which is the joke here.
Oh so maybe you think the cable is pinching then?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Acceptable readings for a NEW installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I don't need to. It was the fact you mentioned there is water between cores which is the joke here.
If this cable is part of the DNO supply then it is not subject to BS7671, it will be whatever the DNO decides is acceptable (EDF in this case).You cant fail it... Its 40x greater than the minimum requirement BS7671.. It could be seen as fraud leading a customer into thinking its not passable!
If its part of the DNO then why are you ir testing this cable?
If its part of the DNO then why are you ir testing this cable?
Probably because they will want the dead test results before they will energise it.
I think I would have investigated further, maybe as far as testing only the cable by itself (after disconnecting and drying the ends) in case it was damaged.
You sure? Please correct me if I'm wrong. 500v test voltage for up to 500 line voltage.
I've been wrong before!