You cant fail it... Its 40x greater than the minimum requirement BS7671.. It could be seen as fraud leading a customer into thinking its not passable!
If this cable is part of the DNO supply then it is not subject to BS7671, it will be whatever the DNO decides is acceptable (EDF in this case).

If this is a lot lower than other identical cables/risers then I would be concerned too, did you try wiping the terminations riser etc. with a dry clean rag ? it is more likely the terminations or the switchgear being damp than between cores, and did you test between all of the cores (all 10 tests) ?
 
I think I would have investigated further, maybe as far as testing only the cable by itself (after disconnecting and drying the ends) in case it was damaged.
 
I think I would have investigated further, maybe as far as testing only the cable by itself (after disconnecting and drying the ends) in case it was damaged.

Yes would have liked to have tested before it was connected. Will check equipment for any flash test results. Not really practical to disconnect now.
 
You sure? Please correct me if I'm wrong. 500v test voltage for up to 500 line voltage.

I've been wrong before!
 
Reg 612 says you are correct.

If I test at 1000V then readings will go up to 500 meg. Test at 500V then readings will go to 299 meg.

With my meggar anyway.
 
Did a long run recently in 120sqmm, measured it on the drum, measured it when buried and lastly when terminated, a bit OTT maybe but had >1999 right up until I terminated on to the customers own fuseboard, then it dropped to 1500. If it was as low as 40M , I would have been pretty upset. If you can get at both ends I would have a good look for dirt etc and perhaps un- bolt the lugs so they are in free air and test again.
 
You sure? Please correct me if I'm wrong. 500v test voltage for up to 500 line voltage.

I've been wrong before!

Only according to BS7671, as this is a DNO cable BS7671 does not apply, I am not sure what the DNO requirements are, but when testing switchgear we used to test at a 1000V (up to Giga ohms) and at 2.5kV for 25 seconds, BS7671 is not the only regs about, don't forget BS7671 is the absolute minimum standard even when that standard does apply
 

Reply to Acceptable readings for a NEW installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
559
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
993
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
925

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top