Adapt this CU........... | Page 2 | on ElectriciansForums

Discuss Adapt this CU........... in the UK Electrical Forum area at ElectriciansForums.net

O

Octopus

OK - this is a dual board, about 3 years old ......... 1 RCD per bank.

They are experiencing random tripping, and my trusty earth leakage clamp shows that both banks are running at around 21 mA leakage - so the smallest change plunges half the house into darkness etc.

Anyone know if I could easily source the parts to add 2 more RCD's (yes I realise some circuit consolidation would be required ....

[ElectriciansForums.net] Adapt this CU...........


Thanks

And no I didn't install this!
 
I had the same issue on a stackable Hager 36 way board. Lots of electronics and control system were leaking due to design.

We added another neutral bar and put rings, cooker and kitchen on rcbo's. Problem went away, I think adding an RCD would be more hassle than it's worth.
 
How does adding another neutral bar solve the problem ?
The only thing that makes sense is that it lowers the neutral systems impedance.
In which case that indicates a failing or poor neutral system to start with.

Adding a neutral bar would enable RCBO's to be added .... then the higher leaking circuits could be on them, reducing the cumulative leakage on the current RCD's.

Having 13 MCB's on RCD wasn't a great idea to start with!
 
How does adding another neutral bar solve the problem ?
The only thing that makes sense is that it lowers the neutral systems impedance.
In which case that indicates a failing or poor neutral system to start with.

Too much earth leakage going through the rcds . adding another neutral bar allows the earth leakage to be split across more devices .
 
never mind, pete, aldi is open till 21.00 hrs. send mrs. pete out. if you're lucky, might get a pie as well.
Not possible for Mrs Pete999 to get about much these days Tel, and to be honest I really can't be bothered, as well as the drink driving issue, I'LL wait till I get back from ELEX tomorrow. Pick up 1 or 6 on the way home.
 

Reply to Adapt this CU........... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top