Hi,

I am looking for some advice on the best way to install 5 double plug sockets into my garage, all of which will be running multiple computers.

My CU is located in the garage.

Would it be best to install the sockets onto their own ring main, or to add them onto the existing garage circuit?

Any advice is appreciated.

Thanks,
Josh.

EDIT: I am only installing the sockets, I will consult an electrician to connect them to the CU if required.
 
How many computers? You say 5 twin sockets, each with multiple computers.
the sockets will need to be protected by an rcd and this could be a problem if you are running more than 10 computers.

I think you should get an electrician to come and specify this because of the possibility of large earth leakage currents.
if your house has a single rcd that protects it, you may well be in darkness regularly.
 
before we can give you the answer, what kind of consumer unit is installed and if so how is the wiring going to be installed.
i'm not sure exactly what CU is installed, see attached image.
The sockets will be on the opposite side of the garage from the CU, so was hoping i'd be able to run 2.5 cable in conduit across the garage ceiling to the CU, and wired into one of the empty slots.
 

Attachments

  • [ElectriciansForums.net] Adding 5 double plug sockets to garage
    PXL_20210818_143342637.jpg
    353.9 KB · Views: 53
How many computers? You say 5 twin sockets, each with multiple computers.
the sockets will need to be protected by an rcd and this could be a problem if you are running more than 10 computers.

I think you should get an electrician to come and specify this because of the possibility of large earth leakage currents.
if your house has a single rcd that protects it, you may well be in darkness regularly.
Currently there are 6 computers, on sockets wired into the upstairs circuit ring main and I have no problems.
I'm moving them into the garage for various reasons.

See image in my previous reply for the CU.
 
Currently there are 6 computers, on sockets wired into the upstairs circuit ring main and I have no problems.
I'm moving them into the garage for various reasons.

See image in my previous reply for the CU.

There are lots of variables here, what size cable is feeding your garage? What type of cable is the feed to the garage? What size is the circuit breaker? Is there any RCD protection, if so where is that protection?

There are also computers then there are computers, do you know what sort of current draw they have?

A lot of garages are fed by a small supply cable as most people just want to plug in say a lawn mower and have lights in the garage, you may need to increase the size of the supply cable.

Having just 6 computers you should be ok on the earth leakage just about but if you ever want to add more it might be worth thinking about a separate circuit for future expansion. If you do need to increase the supply cable think about also if you would ever want to put a car charger on the garage wall. What about any possible heaters in the garage?

I know it just seems like you add some more sockets but it really depends on the load requirement and what is currently in place, nobody on a forum can really tell you that so you need an electrician.
 
If you can, I would suggesting running some SWA cable from your house CU to the garage CU and feeding it off a non-RCD MCB at the house. That allows you the option to have 2 or more radial circuits in the garage, each on separate 20A RCBOs if you do encounter problems of high leakage tripping things.

On a hard fault you won't get selectivity, as the "instant" trip of the supply MCB will easily be reached by such a fault before the down-stream MCB/RCBO has any chance to clear it, but that might be an acceptable situation for you. If not it means a slightly more expensive job to have a fused-switch feed the SWA from the supply before the house CU (i.e. independant of the house CU).

Newer computers are not too bad, typically they are only 0.5-1mA or so and 6 double sockets will be passable off one 30mA RCD (recommendation is you design for no more than 10mA leakage on any circuit normally), but start adding UPS and extension blocks for odd extras and the future is murky...

Where you might see it trip is if there are any voltage disturbances so you get a high dV/dt on the supply and all that capacitance pushes things over the edge.
 
Also to add, you might want to consider lights in the garage with battery back up in case power does go off and you are plunged in to darkness. You can get LED batton lights with that built in for only £40 or so extra.
I used to put non maintained EM lights in garages and workshops that had , or likely to use rotary machines or the like.
 

Reply to Adding 5 double plug sockets to garage in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Also Merry Christmas and Happy New Year from Electricians Forums. :) I think 2025 should see some house building going on which will free up...
    • Like
Replies
1
Views
80
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
728
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
1K

Similar threads

Are you sure the existing outside socket is on the ring, and not already a spur? I tend to place a switch fuse on the ring inside so that the...
Replies
1
Views
162
Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
383

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top