what's your take on adding circuits to a full DB.
Warehouse unit,3p DB,full to capacity,new 3p circuit to be added,client refuses to upgrade DB.
Would you reconfigure a couple of circuits to allow for this new circuit.
 
Davesparks just beat me to it, not a good idea to feed one board from another via an mcb.
It only needs a decent fault on the new board and it could easily trip the whole board.
 
Sub board off the existing board for me, not a henley block. Then move a few circuits over to the new board to make way for the submain breaker.
The OP only needs to install one circuit, if he can gain enough space for an MCB to feed a sub-board he wont need a sub-board!

I think it's rather silly to dismiss the idea of grouping together one or two circuits to gain enough ways, without knowing the loads/circuits involved it may be a perfectly viable option. There seems to be a trend on this forum of late to dismiss common sense solutions to a simple problem as a bodge, and advocate 'walking away' if the client wont pay for the perfect end product. Perfect is not always required as long as a solution is safe, compliant and keeps the customer satisfied.
 
Last edited by a moderator:
what's your take on adding circuits to a full DB.
Warehouse unit,3p DB,full to capacity,new 3p circuit to be added,client refuses to upgrade DB.
Would you reconfigure a couple of circuits to allow for this new circuit.
Ah sorry about my post regarding a 13 Amp socket reread your post and it's a new 3 phase circuit that is required sorry if I confused the issue, my bad.
 
The OP only needs to install one circuit, if he can gain enough space for an MCB to feed a sub-board he wont need a sub-board!

I think it's rather silly to dismiss the idea of grouping together one or two circuits to gain enough ways, without knowing the loads/circuits involved it may be a perfectly viable option. There seems to be a trend on this forum of late to dismiss common sense solutions to a simple problem as a bodge, and advocate 'walking away' if the client wont pay for the perfect end product. Perfect is not always required as long as a solution is safe, compliant and keeps the customer satisfied.
Agree,& that may be the logical way to go,I doubt very much the client is gonna be happy with the idea of a new Db & costs.
If we walk away from it,no doubt someone will do it.
All will be noted on the certificate,so will pass the onus back onto the customer.
 
The OP only needs to install one circuit, if he can gain enough space for an MCB to feed a sub-board he wont need a sub-board!

I think it's rather silly to dismiss the idea of grouping together one or two circuits to gain enough ways, without knowing the loads/circuits involved it may be a perfectly viable option. There seems to be a trend on this forum of late to dismiss common sense solutions to a simple problem as a bodge, and advocate 'walking away' if the client wont pay for the perfect end product. Perfect is not always required as long as a solution is safe, compliant and keeps the customer satisfied.
well said tooth puller ,I could not say better me self.:D
 

Reply to Adding circuits to a full DB in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
931
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
801
Unless the circuit is new or has recently been tested/certified by a.n.other, I'm not sure how you prove the circuit is 'safe' to connect to...
Replies
1
Views
277

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top