I've a possible job coming up where I'd need to add a circuit to a domestic property which has several spare ways both protected by 30mA rcd's the circuit I will be installing can't go on a 30mA rcd and will be surface ,usually in conduit/trunking and so I'll get a split load kit for it and add it next to the main switch and change the labelling etc
this is a problem I've had before in which case I've installed a one way consumer unit but occasionally there is no space for this

So the question is if you have this scenario on a consumer unit where you can't source the correct kit ,is it acceptable to take a flexible tail direct from the outgoing main switch side to the Mcb and lose one of the spare ways from the Rcd side and fit a neutral block to the back of the consumer unit and place the new circuit Mcb in the middle of the CU ie between the Rcd protected circuits ( to avoid reconfiguring the whole board ) assuming that its clearly labelled as a non Rcd circuit
It seems a bit of a bodge and was suggested by an another Electrician quoting for the same job ,but could be a solution and I'm interested to hear any views on this.
 
You could convert one of the RCD's (with the least number of MCB's) to RCBO's and add the MCB to that neutral. May be a bit pricey depending on the number of MCB's to convert.

You may be able to move some of the MCB's across to the other RCD to reduce the cost.
 
Last edited:
This is not the issue the circuit will be run surface ! (assuming TN system TT it would go on a 100mA Rcd) therefore no Rcd protection required
As for the IP rated box if i can use one of these then I could probably fit a one way Cu in the same space in the op the point was that space was limited
 
Last edited:
This is not the issue the circuit will be run surface ! (assuming TN system TT it would go on a 100mA Rcd) therefore no Rcd protection required
As for the IP rated box if i can use one of these then I could probably fit a one way Cu in the same space in the op the point was that space was limited
Yes well we have this problem loads ...tryin to get an RCD board to cover our work next to BS3036s and stuff.....you could put another section of neutral bar as TQ sugests so in a way its like a high integrity and take a feed from the incomer....
 
I've a possible job coming up where I'd need to add a circuit to a domestic property which has several spare ways both protected by 30mA rcd's the circuit I will be installing can't go on a 30mA rcd and will be surface ,usually in conduit/trunking and so I'll get a split load kit for it and add it next to the main switch and change the labelling etc
this is a problem I've had before in which case I've installed a one way consumer unit but occasionally there is no space for this

So the question is if you have this scenario on a consumer unit where you can't source the correct kit ,is it acceptable to take a flexible tail direct from the outgoing main switch side to the Mcb and lose one of the spare ways from the Rcd side and fit a neutral block to the back of the consumer unit and place the new circuit Mcb in the middle of the CU ie between the Rcd protected circuits ( to avoid reconfiguring the whole board ) assuming that its clearly labelled as a non Rcd circuit
It seems a bit of a bodge and was suggested by an another Electrician quoting for the same job ,but could be a solution and I'm interested to hear any views on this.

One thing to watch out for with the highlighted bit is the cable you take from the main switch, don't be tempted to stuff a bit of 2.5mm2 in there, or most other sizes in fact - chances are they will not have the CCC to match the only protective device back down the line - the main fuse. I'm assuming there's nothing else inbetween.
 
Absolutely agree with that it would only be done with same size tails as existing,and only if there was capacity in the terminal for another ,However the non conforming to a British standard is a problem when its an old unit,ie getting the ok from the manufacturer

Its actually a Pv job cables either surface conduit or Swa so no need for RCD (tn system)
 
One thing to watch out for with the highlighted bit is the cable you take from the main switch, don't be tempted to stuff a bit of 2.5mm2 in there, or most other sizes in fact - chances are they will not have the CCC to match the only protective device back down the line - the main fuse. I'm assuming there's nothing else inbetween.

Interesting that you say that as I would always do the same BUT- Wylex make specific PV board now with a mcb, double pole isolator and a generation meter all within a 17th edition board. The problem being that "they" at manufacturing stage have linked the primary main switch to the PV mcb in what looks like no bigger than 4mm. Strange!
 

Reply to Adding non Rcd protected circuit to split consumer unit in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
844
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
967

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top