adding shower CU | on ElectriciansForums

Discuss adding shower CU in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jan 21, 2011
Messages
581
Reaction score
57
hi

just wanted to check something,
when adding a seperate shower CU (split tails) from a 80amp or even 100amp main supply the tails feeding the shower CU do they have to now be 25mm? or will 16mm be adequate due to the fixed load of the shower

The seperate shower cu (63amp 30ma RCD) is this again due to the CU supplying one fixed load so no need to be rated at the 100 or 80amp supply fuse

many thanks
 
its ok now have it sorted, 11kw shower will only draw 47.8 amps max so the 63amp rcd is fine.

same for tails supplying shower CU max of 47.8amps so 16mm would be fine. got confused with minimum of 25mm for MAIN TAILS for above 60amp main fuse
 
11kW shower makes a complete mockery of fitting energy saving lamps. how many low energy lamps would it take to recoup the extra, non-essential 3kW in that shower.?
 
11kW shower makes a complete mockery of fitting energy saving lamps. how many low energy lamps would it take to recoup the extra, non-essential 3kW in that shower.?


That 3kw will probably never be used, mostly down to humans having that issue with excessive heat

Anyway, Looking at the manufactures cables inside the average shower I'd say none of them will ever draw anything close to that and manufactures are just playing it safe
 
if you split the mains tails and the incoming fuse is 80amp your new cu for the shower main switch would have to be 80amp rated 16 mm tails are sufficient

so why do all of the shower rcd units come with a 63A rcd/mainswitch doesnt make any sense especially as most shower manufactures state there showers must be connected to at least an 80amp mainswitch also
 
Last edited:
by backfusing Lenny are you saying that the cable feeding the shower CU (if under 3 meters) is protected by the MCB in the shower CU lets say 40amps for a 8.5KW shower.

i agree reg not very clear
 
Last edited:
Yip! Stick in 10mm tails if you have them.

Seen on a few sites the fire alarm on the mains panels fed directly off the busbar in 1.5/2.5MM cable. 1000Amp supplies to the panel and the like.
 
I think what he is saying is if the feed ie 16mm tails are over 3m from the origin then you will need a KMF switch at the origin of supply.
So if your shower CU is in the airing cupboard or something and over 3m from the origin of supply you will need a isolator/KMF switch.
 
yes i agree snapster, if the shower cu is within 3 meters no need for a switchfuse to protect the 16mm tails. the way i see it they would be protected via the mcb/rcd in the new shower cu. if over 3 m the 16mm tails would have to be protected and fused down via a switchfuse at origin before beeing routed to shower cu.

so i think that the 16mm tails can feed the 63a/30ma rcd mainswitch of the shower cu directly from the 80amp/100amp main fuse via henly block.
 
As long as your reduced fuse or breaker is within 3M of the supply point, then the cables only need rating at the new fuse/breaker. Hence, if your new shower CU had a 40A MCB installed and that is therefore the maximum current which can flow through that system, then 10mm tails would suffice (or 63a/16mm). As said previously tho, the RCD rating is NOT your circuit protection. You will need an additional MCB or RCBO
 
Last edited:

Reply to adding shower CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
The norm is that it goes from the DSO (ESB) fuse to a DSO isolator with a contractor's side, and then to the main overcurrent device. The ESB...
Replies
9
Views
3K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
667
In years gone by many of us would feed an additional small CU [say for a shower or outbuilding for example] with 6mm tails, often directly...
Replies
6
Views
2K
  • Question
Most decent electricians will be very wary of connecting cables which have been installed by someone else because they have no way of knowing how...
Replies
9
Views
6K
davesparks
D
  • Question
Although that might make the trunking bigger than it needs to be even for sheathed singles, and enforces a proper complete run of trunking from...
Replies
12
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks