hi

just wanted to check something,
when adding a seperate shower CU (split tails) from a 80amp or even 100amp main supply the tails feeding the shower CU do they have to now be 25mm? or will 16mm be adequate due to the fixed load of the shower

The seperate shower cu (63amp 30ma RCD) is this again due to the CU supplying one fixed load so no need to be rated at the 100 or 80amp supply fuse

many thanks
 
its ok now have it sorted, 11kw shower will only draw 47.8 amps max so the 63amp rcd is fine.

same for tails supplying shower CU max of 47.8amps so 16mm would be fine. got confused with minimum of 25mm for MAIN TAILS for above 60amp main fuse
 
11kW shower makes a complete mockery of fitting energy saving lamps. how many low energy lamps would it take to recoup the extra, non-essential 3kW in that shower.?
 
11kW shower makes a complete mockery of fitting energy saving lamps. how many low energy lamps would it take to recoup the extra, non-essential 3kW in that shower.?


That 3kw will probably never be used, mostly down to humans having that issue with excessive heat

Anyway, Looking at the manufactures cables inside the average shower I'd say none of them will ever draw anything close to that and manufactures are just playing it safe
 
if you split the mains tails and the incoming fuse is 80amp your new cu for the shower main switch would have to be 80amp rated 16 mm tails are sufficient

so why do all of the shower rcd units come with a 63A rcd/mainswitch doesnt make any sense especially as most shower manufactures state there showers must be connected to at least an 80amp mainswitch also
 
Last edited:

Reply to adding shower CU in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
984

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top