hi

just wanted to check something,
when adding a seperate shower CU (split tails) from a 80amp or even 100amp main supply the tails feeding the shower CU do they have to now be 25mm? or will 16mm be adequate due to the fixed load of the shower

The seperate shower cu (63amp 30ma RCD) is this again due to the CU supplying one fixed load so no need to be rated at the 100 or 80amp supply fuse

many thanks
 
thankyou guitarist thats what i was thinking, so would you agree that as the shower cu can only draw 40amps the shower CU 63a/30ma rcd switch is adequate ?? no need to replace with a 80a/30ma

As long as that is all the CU is able to do, ie. 1 MCB, then yes. Just to reiterate, the 63A main RCD switch will not give you protection against overload and/or short circuit unless it is an RCBO. That said, even if it were, you would still need an appropriate MCB (40A depending on circuit characteristics) to protect your shower cable if it's only 10mm.
 
yes but in the shower cu's its the main switch for the cu so i was concerned at it beeing rated (63a)below the main fuse which might be 80 or 100 amps. but as a shower is a fixed load i guess 63amps will be fine on a 40a or 50a MCB
 
by backfusing Lenny are you saying that the cable feeding the shower CU (if under 3 meters) is protected by the MCB in the shower CU lets say 40amps for a 8.5KW shower.

Essentially, yes.

Its the same principal as taking a feed off a busbar chamber for example.

It may be a 400A chamber, doesn't mean every cable taken from it needs to be rated at 400A, as long as there is a fuse within 3M, the supply cables can then be rated to that fuse size.



Sent from my BlackBerry 9800 using Tapatalk
 
Last edited by a moderator:
Basically forget the 63amps it is only what the switch will work safley at and what max current can pass through it, the 40amps will protect the shower cable not the main incoming feed!
 
yes the mcb will protect the shower cable but i was mistakenly thinking that the rcd switch/current rating would have to be 80 amps for a 80amp supply fuse but if it is a fixed load of only 45amps then thats the maximum the rcd would need to be rated at.
 

Reply to adding shower CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
The norm is that it goes from the DSO (ESB) fuse to a DSO isolator with a contractor's side, and then to the main overcurrent device. The ESB...
Replies
9
Views
3K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
667
In years gone by many of us would feed an additional small CU [say for a shower or outbuilding for example] with 6mm tails, often directly...
Replies
6
Views
2K
  • Question
Most decent electricians will be very wary of connecting cables which have been installed by someone else because they have no way of knowing how...
Replies
9
Views
6K
davesparks
D
  • Question
Although that might make the trunking bigger than it needs to be even for sheathed singles, and enforces a proper complete run of trunking from...
Replies
12
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks