Hi.

I have a radial circuit supplying electricity to the garage (part of the house). It's on a 20amp breaker, uses 2.5mm cable. It currently only supplies a single socket. Before anyone asks, its 100% a radial circuit. 6 months ago I had an electrician install a new consumer unit, and the testing/certificate that followed states this.

There is a single socket on the circuit. Annoyingly, the socket is at the back of the garage and right in the middle of the wall.

What I would like to do is keep this socket. Then... come out of the socket on the left, and put a socket on the left wall, and out of the right and put a socket on the right wall. I cant continue the cable round in a single direction as the garage door and other things are is in the way. Coming off in both directions from this socket it the only option.

Would this be ok? An alternative I had was to come out of the the top of the socket into a junction box (30A), then the two cables come out of this... best described as a T junction.

In case anyone wondered, there will not be any high load appliances used. One will supply the chargers for my tool batteries, the other will be Christmas lights!

Thanks in advance.

F
 
Junction boxes are to be avoided if possible,
Agree in principle. But in this case the JB will be in the garage so won't look awful and will be accessible. For an amateur I would imagine connecting three 2.5,s into a JB and looping a 2.5 out to the socket would be easier than connecting the three 2.5,s into the socket
 
As above, if you are competent then adding sockets to this 20A radial is fine. However, you must have some means of testing the results. Spending the ÂŁ500-1500 that an electrician would on a MFT is somewhat out of the question, but at the very least get something like this to check the socket is wired correctly and the earth loop impedance is at least sensibly low:

I also would agree with @LastManOnline to avoid 3 leads in socket terminals, they should go but you need care that all 3 are fully engaged and gripped. Putting a junction box in the garage should be fine, if it were me I would use something like the 3-way or 5-way Wago 221 series terminals for the connections in something like a Wiska 407 box. You can also get glands like these for T&E cable for a good mechanical support:
 
Let's not confuse the two questions of legally being able to do the work, and the requirement (or not) to notify the work.


“No person shall be engaged in any work activity where technical knowledge or experience is necessary to prevent danger, or where appropriate, injury, unless he/she possesses such knowledge or experience, or is under such a degree of supervision as may be appropriate having regard to the nature of the work.”
(Electricity at Work Regulations 1989 (EAWR) – Regulation 16)

If you meet the bit in bold then it's legal for you to do the work.
As @brianmoooore said all electrical work should be tested and documented and if you're not providing a new circuit the Minor Works Certificate can be used instead of the more complex Electrical Installation Certificate.
A very informative thread for me this. Can I conclude that in the UK an unskilled person can theoretically buy a multimeter, a set of electricians tools etc and then rewire and certify a house?
 
A very informative thread for me this. Can I conclude that in the UK an unskilled person can theoretically buy a multimeter, a set of electricians tools etc and then rewire and certify a house?

No because they would not have the equipment (which would need to be an MFT, not a multimeter) or the ability to do the testing or complete the installation cert. Also a new consumer would need notifying to building control (admittedly a non-electrician can sometimes do this)
 
I would like to slightly clarify a statement I made:
The OP asked whether it was legal, we said yes, crack on.
I did not intend to convey it is legal in all cases.
I intended to convey that it is legal subject to the persons knowledge and experience, as per my my earlier quote from the EAWR.
(My impression is that the OP has the ability to do this safely and competently)

A very informative thread for me this. Can I conclude that in the UK an unskilled person can theoretically buy a multimeter, a set of electricians tools etc and then rewire and certify a house?
A multi-meter won't be accurate enough in terms of resolution for continuity tests and won't be able to test earth loop impedance, insulation resistance, or time RCD activation/operation. As mentioned above the cost of such tools and knowledge to use them safely is a barrier to most people entertaining this.
Of course anyone can theoretically do anything, but the EAWR which is the statutory legal document does indicate knowledge and experience is required.

That's before you get onto the building regs requirements, as a new consumer unit and new circuits are notifiable works, which generally means membership of one of the competent person schemes and they have their own entry requirements which are getting harder not easier.
So it isn't as simple as you suggest.
 
No because they would not have the equipment (which would need to be an MFT, not a multimeter) or the ability to do the testing or complete the installation cert. Also a new consumer would need notifying to building control (admittedly a non-electrician can sometimes do this)
Interesting. Yet posts 4,6,12 indicate that anyone can legally carry out the work and certify PROVIDING they are competent to do so.?
 
Interesting. Yet posts 4,6,12 indicate that anyone can legally carry out the work and certify PROVIDING they are competent to do so.?
That is my understanding of the law, however, for local building control they would normally require membership of a CPS to establish competence, otherwise they would require (and probably arrange at the requester's expense) a 3rd party to certify the work.

But not all LBC are the same and some are OK with electricians who are not in a CPS if experience, qualifications, etc, are good. For example, a few industrial/commercial sparks are not members as they don't feel the fees are justified and they are not a requirement outside of domestic work. Competence is always required! (Plus the usual test equipment, insurance, generation of certificates, etc)
 
Interesting. Yet posts 4,6,12 indicate that anyone can legally carry out the work and certify PROVIDING they are competent to do so.?

Yes, they can. But anyone who is competent enough to test and fill in installation certs is probably an electrician. Or in rare cases a very keen DIYer.

I think that's been made clear.
 
Interesting. Yet posts 4,6,12 indicate that anyone can legally carry out the work and certify PROVIDING they are competent to do so.?
Yes. If you accept that part of being competent is knowing what equipment is required to obtain and understand the detailed data that the certificate requires and being able to access and use such equipment. Including knowing what test results constitute a safe installation or a dangerous situation.

If you are competent you can do electrical work and issue certificates.
In a parallel universe certain work needs notifying to building control as per earlier posts. If you avoid such work and are competent you can do what you like.
 
Last edited:
No because they would not have the equipment (which would need to be an MFT, not a multimeter)
Apologies for stating "multimeter" instead of MFT. It caused an un-necessary distraction
Also a new consumer would need notifying to building control (admittedly a non-electrician can sometimes do this)
I am trying to get my head around the UK system. When you state "admittedly a non-electrician can do this" I, m left with the impression there are a number of grey areas in the regulation of electrical work in the UK and I, m keen to understand them.
 
Apologies for stating "multimeter" instead of MFT. It caused an un-necessary distraction

I am trying to get my head around the UK system. When you state "admittedly a non-electrician can do this" I, m left with the impression there are a number of grey areas in the regulation of electrical work in the UK and I, m keen to understand them.

Anyone competent can do electrical work. But the work must be tested and then either a minor works or an installation cert should be completed.

Some work (new circuits, consumer unit swaps, etc) also needs notifying to building control. For this you either need to be in a scheme such as the NIC etc. or pay the council a fee.
 
Anyone competent can do electrical work. But the work must be tested and then either a minor works or an installation cert should be completed.

Some work (new circuits, consumer unit swaps, etc) also needs notifying to building control. For this you either need to be in a scheme such as the NIC etc. or pay the council a fee.
So from the above can I conclude that in principle someone with no formal electrical training and who is not a member of any scheme, but is a capable diyer.. can do the work, certify (having bought an MFT) and pay the council a fee (as he is not joined any scheme) and is done and dusted??
 
So from the above can I conclude that in principle someone with no formal electrical training and who is not a member of any scheme, but is a capable diyer.. can do the work, certify (having bought an MFT) and pay the council a fee (as he is not joined any scheme) and is done and dusted??

Theoretically. But how would someone know how to perform IR, RCD, Zs, PFC tests etc. Let alone have an MFT and know how to use it. And to be competent you would need all this.
 
So from the above can I conclude that in principle someone with no formal electrical training and who is not a member of any scheme, but is a capable diyer.. can do the work, certify (having bought an MFT) and pay the council a fee (as he is not joined any scheme) and is done and dusted??
It's also worth noting that
1) the council will charge at least a couple of hundred quid for the privilege.
2) some councils don't offer the service at all even though they are supposed to.
I know a very capable DIY'er who attempted to use this service in the Dudley area and got no engagement at all from the council.

From a sparks point of view, as a scheme member it costs me ÂŁ3.60 to notify the work.
So if you do enough domestic work it pays to be in the scheme as otherwise the high cost has to be passed onto the customer, leading them to someone else's quote so you simply don't get the work.
 
Theoretically.
That was in fact the original question I asked. Appreciate your answer.
But how would someone know how to perform IR, RCD, Zs, PFC tests etc. Let alone have an MFT and know how to use it. And to be competent you would need all this.
Of course that is true. But we all occasionally come across individual's who fall in to the "overconfident and undertrained" department and given an opening are happy to take it. Your system would benefit from losing off that loophole.
 

Reply to Adding sockets to a radial circuit in different directions in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
855

Similar threads

  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K
I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
470

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top