well Ive joined the NEC forum and sent a post about adding a testing procedure section to the code book
heres the post.

I know that testing procedures are taught in apprenticeship but Ive found it to be severely lacking in clarity and tends to be an issue with many apprentices not being taught properly.
I would like to see a section in the codes that covers proper testing procedures and standard practices as well as proper documentation of results.
there should be no question on what procedures to follow and how to carry them out

we'll see if it flies or goes over like a lead balloon
 
You need to mention the correct sequence in which these tests should be conducted and what tests you'd like to see incorporated??

So, ...how are you getting on with the new Earth Loop Impedance meter you recently purchased?? What was the on-line English manual link like that gave you?? Was it more Chinglish than English?? lol!!
 
love it it works great
our local inspector is happy that ive got one
and i'll probably be getting a lot of calls from him
got the manual in english and have located a company that will do the calibration if
and i saved the testing sequence you fellas have posted before as a reference for them
 
love it it works great
our local inspector is happy that ive got one
and i'll probably be getting a lot of calls from him
got the manual in english and have located a company that will do the calibration if
and i saved the testing sequence you fellas have posted before as a reference for them

Any chance of posting that English link for the manual gnuuser, i'd be interested to see it??
 
Sorry gnuuser, but that tester isn't an Earth Loop Impedance meter, it's a straight foward 3 point earth/ground resistance meter!! Check out the forum sponsor website at the top of the page to see various ELI meters and their function. (test-meter.co.uk)

ok will check it out later
have to go see my father
went to hospital last night
 
yes hes doing ok , a bit sore though
had a cellulitis infection and infected bursa under the knee cap
they drained it and have him on a strong anti-biotic




ill probably get this meter as it will probably suit the need better for loop testing.
http://www.test-meter.co.uk/martindale-ez2500-e-ze-test/

but the ground resistance meter will still come in handy for new installation (more tests and happier inspectors)
 
Last edited:
yes hes doing ok , a bit sore though
had a cellulitis infection and infected bursa under the knee cap
they drained it and have him on a strong anti-biotic




ill probably get this meter as it will probably suit the need better for loop testing.
Martindale EZ2500 E-Ze Test Non-Trip Loop Tester, EZ-2500 16th Edition Tester

but the ground resistance meter will still come in handy for new installation (more tests and happier inspectors)

Very handy, as TT earthing is almost the norm in many areas of the States!! Not just for new installations either, also use to test existing earth electrodes at various times of the year (Spring / Summer/ Winter) to check for stability of the electrode.


Not sure that particular ELI meter will be suitable for you in the States. Try looking for a budget meter that is suitable for your 120/240v system and supplied with test leads (rather than just a receptacle plug top) that's available in the States. Possibly from the same Chinese manufacturer as the earth tester you recently purchased (not all Chinese products are cheap tat (crap), some are well made bits of kit). Oh and forget about the no-trip function, this is for 30mA GFCI's not your 5/6mA GFCI breakers!! lol!!

Glad to hear the old boy's on the mend!! lol!!
 
Last edited by a moderator:
Very handy, as TT earthing is almost the norm in many areas of the States!! Not just for new installations either, also use to test existing earth electrodes at various times of the year (Spring / Summer/ Winter) to check for stability of the electrode.


Not sure that particular ELI meter will be suitable for you in the States. Try looking for a budget meter that is suitable for your 120/240v system and supplied with test leads (rather than just a receptacle plug top) that's available in the States. Possibly from the same Chinese manufacturer as the earth tester you recently purchased (not all Chinese products are cheap tat (crap), some are well made bits of kit). Oh and forget about the no-trip function, this is for 30mA GFCI's not your 5/6mA GFCI breakers!! lol!!

Glad to hear the old boy's on the mend!! lol!!


You mean the United states? TT earth is absolutely forbidden in the United States. In fact it has never been used, most electricians haven't even heard of it.
 
You mean the United states? TT earth is absolutely forbidden in the United States. In fact it has never been used, most electricians haven't even heard of it.

Really, Perhaps you can explain to us why this earthing method is described in in NFPA 70 (NEC) and even gives a maximum Ra value of 25 ohms for a single earth rod, or a second rod must be provided.
So either you don't know or unfamiliar with the term ''TT'' system, (which i suspect is the case here), or you haven't a clue what you're talking about.... because earth (ground) rods are probably the most prominent means of providing and earth (ground) point, especially for domestic installations in USA. Now tell me that again that TT earthing (grounding) systems is absolutely forbidden, and has never been used??

Perhaps i'd better explain that i've worked on several large overseas projects over the years where your NEC has been the Specifications electrical standard, so i'm more than well versed in it's content, as well as the electrical red, green, buff etc books !!
 
Really, Perhaps you can explain to us why this earthing method is described in in NFPA 70 (NEC) and even gives a maximum Ra value of 25 ohms for a single earth rod, or a second rod must be provided.
So either you don't know or unfamiliar with the term ''TT'' system, (which i suspect is the case here), or you haven't a clue what you're talking about.... because earth (ground) rods are probably the most prominent means of providing and earth (ground) point, especially for domestic installations in USA. Now tell me that again that TT earthing (grounding) systems is absolutely forbidden, and has never been used??

Perhaps i'd better explain that i've worked on several large overseas projects over the years where your NEC has been the Specifications electrical standard, so i'm more than well versed in it's content, as well as the electrical red, green, buff etc books !!

That has absolutely nothing to do with clearing a fault. Tell me, since you are so versed, using ohms law: how does 25 ohms generate enough fault current to trip a non RCD breaker, which accounts for 99.99% of American breakers?

And if you are so well versed in the NEC, you would know more than well that a bonding jumper is required at every American service where a neutral is present.

To tell me who lives in the US, spent decades applying the NEC, and working with power systems first hand that TT earthing is routine in the USA is beyond arrogant.

If you are wiring power system as TT overseas using NFPA 70 you are going to get someone killed if you have no already. Perhaps that is why I hear so much stories of people being electrocuted overseas. Your line thinking is beyond mortifying.
 

Reply to adding test procedures to the NEC code in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
346
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
885
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top