My mate has an old wylex board with the push in rewireable fuses; and has asked about fitting an rcd to one circuit (a ring main) that supplies one outside socket (at the mo he's using a plug in portable rcd when using the mower). He does not want a new consumer unit, and i know that rcbo's are not compatible with these old fuseboards so thats not an option; a rcd spur to the outside socket is not an option either because that means taking out the kitchen sink to access the ring where it loops outside. Therefore he wants to protect the whole circuit with an rcd located near the fuseboard.

Could I take one leg of the ring via the rcd and leave the other leg in the fuseboard, or would both legs of the ring need to go through the rcd ?

Thanks
 
Last edited:
Cheapest option would be to find said socket he's plugging his lawn mower into and replace the socket faceplate with an RCD socket.

Why would you only take one leg off the circuit? presumably you'll be installing the RCD at or near the CU ?
 
how you do this is to take both the L and N legs of the RFC out of the fuse and N bar. extend with in line connectors to reach RCD in an enclosure adjacent to the CU. then you feed the RCD from the fuse and the N bar with a couple of bits of 6mm stripped out of some 6mm T/E . you're then responsible for the whole circuit. test and then fill in a MWC
 
Cheapest option would be to find said socket he's plugging his lawn mower into and replace the socket faceplate with an RCD socket.

Why would you only take one leg off the circuit? presumably you'll be installing the RCD at or near the CU ?

That is another way to do it, but he might aswell have the entire circuit protected. Im thinking of adding an rcd into the circuit just after it leaves the fuseboard, just not sure if both ends of the ring need to go through the rcd, or just one. Im assuming the rcd would still operate if just one side of the ring went through it.
 
how you do this is to take both the L and N legs of the RFC out of the fuse and N bar. extend with in line connectors to reach RCD in an enclosure adjacent to the CU. then you feed the RCD from the fuse and the N bar with a couple of bits of 6mm stripped out of some 6mm T/E . you're then responsible for the whole circuit. test and then fill in a MWC

So you mean feed the supply side of the rcd with a 6mm radial from the fuse and connect the existing two legs of the ring to the load side ? Why couldn't I just divert one leg of the ring via the rcd ? Which im not sure about so this really is why im asking. If only one leg of the ring went via the rcd then would the whole circuit be protected ? or not ? if you see where im coming from !
 
So you mean feed the supply side of the rcd with a 6mm radial from the fuse and connect the existing two legs of the ring to the load side ? Why couldn't I just divert one leg of the ring via the rcd ? Which im not sure about so this really is why im asking. If only one leg of the ring went via the rcd then would the whole circuit be protected ? or not ? if you see where im coming from !
Are you a qualified electrician?
 
An rcd measures any imbalance between line & neutral, so how be the principles that it would trip if rcd was connected to just one leg of the ring. Thanks telectrix for noting it will trip which I take your word for it, just dont see how this is immediately.
 
haptism, I don't won't to appear rude, but you post #4 suggest you are not a qualified electrician. At the moment your mate is safely using his mower with a plug in RCD. If you alter the ring final circuit he uses for his mower, and don't get it correct, it an have potentially dangerous consequences for your mate. I note from your profile you have a C&G 2360 and 16th ed?
 
An rcd measures any imbalance between line & neutral, so how be the principles that it would trip if rcd was connected to just one leg of the ring. Thanks telectrix for noting it will trip which I take your word for it, just dont see how this is immediately.

In a ring final circuit, the current drawn at each outlet (socket, FCU, etc) is split between the two legs of the circuit. Since the L and N of one leg is roughly the same resistance (and same for the other leg) then roughly the L and N of each leg have the same current flowing. But not exactly so, small differences such as cable tolerances, poor connections, will cause a slight imbalance. As soon as the imbalance reaches 30mA (actually maybe 20-odd mA) the RCD will trip. With a 30A load on the circuit, an imbalance of just 0.1% will cause tripping.

And once it has tripped, the circuit will still be live via the other leg, and the cable potentially overloaded since a single 2.5mm T&E is not rated to 30A.
 
Last edited:
haptism, I don't won't to appear rude, but you post #4 suggest you are not a qualified electrician. At the moment your mate is safely using his mower with a plug in RCD. If you alter the ring final circuit he uses for his mower, and don't get it correct, it an have potentially dangerous consequences for your mate. I note from your profile you have a C&G 2360 and 16th ed?


Yes thats right I do; instead of just taking someone word for it and doing things parrot fashion thought I would continue and ask why an rcd on just one leg of a ring would trip. My reasoning is there would be proportional current draw through both lines of a ring to a load, and therefore proportional return currents via neutral, so in this instance why should it trip. As Rob said, what would happen if there was a fault and it did trip, answer it would still be energized. So that is an answer in itself. At least im a bit wiser now. Guys lay off the persecution its all good stuff.
 

Reply to additional RCD protection from old Wylex fuse oard in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I seem to find two types of installation in older houses in which electric showers have been added: those with shower fed from an MCB without RCD...
Replies
9
Views
869
nicebutdim
N
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
707
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top