Ok new house. New install cert issued. However, no supplementary bonding that I can see and accessible .
There is a 10mm earth wire connected above the water stop cock point of entry under the kitchen sink.
However, no cross bonding to the hot pipe.
According to install cert the cross bonding has been ticked off as acceptable condition.
Dual RCD consumer fitted. PME earthing.
Should cross bonding be carried out? Can the electrician by testing, say it's not required?
I understand that in bathrooms, provided all circuits are protected by RCD additional supplementary bonding may not required as long as the electrician can prove by testing, not required.
I would of thought that the hot pipe under the sink, should be bonded. I'm old school.
Thanks